Question: WinCC_OA_3.18_windows_x64_P014 - S7Plus Driver Error

30.04.2026 18:05 by Michelini Alessandro

Hi all,
I try to make this driver running but get as a result the following from LogViewer:
WCCILpmon (1), 2026.04.30 17:52:37.396, SYS, INFO, 24/pmon, Got START command from ::1, starting the manager WCCOAs7plus(3) at index 10
WCCILpmon (1), 2026.04.30 17:52:37.401, SYS, INFO, 1, Manager Start, C:\Siemens\Automation\WinCC_OA\3.18\bin\WCCOAs7plus.exe -PROJ basic_training -pmonIndex 10 -num 3
WCCOAs7plus (3), 2026.04.30 17:52:37.555, SYS, INFO, 1, Manager Start, PROJ, basic_training, V 3.18 - 3.18 platform Windows AMD64 linked at Nov 18 2022 20:30:09 (d9be82d280d)
WCCOAs7plus (3), 2026.04.30 17:52:37.559, PARAM,SEVERE, 68/s7plus, S7PlusDrv, start_oms, Error not coming from OMS+ (-9223281722282473910)
WCCOAs7plus (3), 2026.04.30 17:52:37.561, SYS, INFO, 2, Manager Stop

Thanks to everyone can give some indication.

Responses (1)

06.05.2026 11:19 by Puchegger, Herbert (DI FA HMI SW ETM PS CC)

First of all I would highly recommend you to upgrade at least to the latest patchlevel 3.18 P034_JANUARY-2026 as you are using a really old patch with P014_NOVEMBER-2022. Additionally you must be aware that our current supported versions are 3.19, 3.20 and 3.21.

That said, this specific OMS+ error code could be related to a bad S7DOS installation. To fix that you should completely uninstall WinCC OA and reinstall it. If it does not work (with the latest patch either) it could be that you might have to remove S7DOS entries from the registry.

Br, Herbert