ModBus Warning Exception code received: EC=1 FC=1

Find and share HowTos to various installations / configurations!
Search

Post Reply
3 posts • Page 1 of 1
jeissonsierrac
Posts: 62
Joined: Wed Jun 03, 2015 9:37 pm

ModBus Warning Exception code received: EC=1 FC=1

Post by jeissonsierrac »

Dear all,

We have two projects with Wincc OA 3.16 P002 but , log viewr shows this warning:

WCCOAmod (2), (Time Stamp), SYS, WARNING, 54, Unexpected state, ModModbusMaster, processResponse, 172.16.83.4: Exception code received: EC=1 FC=1 for UA: 1 Ref: 0
WCCOAmod (2), (Time Stamp), SYS, WARNING, 54, Unexpected state, ModModbusMaster, processResponse, 172.16.83.4: Exception code received: EC=1 FC=1 for UA: 1 Ref: 0
WCCOAmod (2), (Time Stamp), SYS, WARNING, 54, Unexpected state, ModModbusMaster, processResponse, 172.16.83.4: Exception code received: EC=1 FC=1 for UA: 1 Ref: 0

Any suggestions to resolve this warning.

Thanks for your help.

mkerk
Posts: 75
Joined: Wed Oct 20, 2010 12:25 pm

Re: ModBus Warning Exception code received: EC=1 FC=1

Post by mkerk »

Hello Jeisson,

In the WinCC OA documenatation in chapter "Drivers" --> Modbus/TCP --> Modbus/TCP driver details" you can find a table, which describes the error meesage of the driver.

the error message "...ModModbusMaster ...Exception code received: EC= .." means the following: Wrong response to a particular request. If too many errors of such kind occur, the connection is closed and reopened.

Please check the connection to the PLC 172.16.83.4 and the state of this PLC

BR,
Mousser

Gertjan van Schijndel
Posts: 634
Joined: Mon Aug 02, 2010 10:37 am

Re: ModBus Warning Exception code received: EC=1 FC=1

Post by Gertjan van Schijndel »

Take a look at this answer from a similar topic.