Hi,
When I restart my project (WinCC OA 3.17 P033) the _address property of all datapoints deletes itself.
I have tried exporting the address and distrib properties with ASCII (using an old project backup) and importing it into the project but no luck, at the moment it loads the property correctly, when I restart the project it deletes itself.
I have also tried deleting and adding the S7Plus Driver and recreating the connection but to no avail.
No error appears in the log.
Thank you all
Filippo
Address config deleted by itself
Search
-
- Posts: 2
- Joined: Tue Apr 05, 2022 9:25 am
Address config deleted by itself
Last edited by filipporossi on Thu Oct 24, 2024 11:47 am, edited 2 times in total.
Re: Address config deleted by itself
I think you only exported the _address configs, but you need to export the _address and _distrib configs.
-
- Posts: 2
- Joined: Tue Apr 05, 2022 9:25 am
Re: Address config deleted by itself
I misspelled, I exported _address and _distrib together
Re: Address config deleted by itself
If the information is gone when restarting the project there is possibly a problem of saving data in the database.
Can you please check if database errors are reported during the ASCII import in the PVSS_II.log file. You can also do an ASCII export in your new project to see which information is saved in the database.
WinCC OA does not delete configs automatically. The creation/deletion of configs is only done on interaction with the system.
Best Regards
Leopold Knipp
Senior Support Specialist
Can you please check if database errors are reported during the ASCII import in the PVSS_II.log file. You can also do an ASCII export in your new project to see which information is saved in the database.
WinCC OA does not delete configs automatically. The creation/deletion of configs is only done on interaction with the system.
Best Regards
Leopold Knipp
Senior Support Specialist