We are using WinCC OA 3.17 Patch 9 on Linux RHEL 8.2.
When using an invalid reference address for a DPE we don't see the invalid bits get set in the para. We do however see the driver reporting the invalid address:
Code: Select all
WCCOAs7plus (2), 2021.08.09 13:02:09.781, PARAM,SEVERE, 72/s7plus, Cannot resolve symbolic address DB_AI_HMI.AEN_AHU_01019_PSX_01.ParHmiDs.parHiHiDlyTm for connection _AEN_BMS_PLC
WCCOAs7plus2:WCCOAs7plus (2), 2021.08.09 13:02:25.003, conn, connError check on connection with name "_AEN_BMS_PLC"
Is this a known bug or are there some config settings we need to apply? We have selected the 'Set invalid bit' on the relevant S7+ connection.
Cheers
Eric