Communication problem ModBus Driver

Find and share HowTos to various installations / configurations!
Search

Post Reply
2 posts • Page 1 of 1
jeissonsierrac
Posts: 62
Joined: Wed Jun 03, 2015 9:37 pm

Communication problem ModBus Driver

Post by jeissonsierrac »

Hello everyone

we have a project, where we must establish communication with a Modbus server, at the time of establishing the communication everything works correctly, but the driver constantly reports loss of communication, reconnection and connection.

this happens with the Wincc OA 3.16 Patch 002, in view of the problem we decided to try the same connection from WinccOA 3.14 Patch 020 and it works correctly the communication is stable and never loses communication.

attached configuration of the equipment in Wincc OA 3.14 and WinCC OA 3.16.


some idea to solve the problem.

Image

https://www.winccoa.com/fileadmin/image ... ccOA_3.png
Attachments
WinccOA_3.png
WinccOA_3.png

Kirvesmies
Posts: 42
Joined: Mon Dec 04, 2017 2:28 pm

Re: Communication problem ModBus Driver

Post by Kirvesmies »

Perhaps the default alive check coil 1 does not get answered. See manual on Possible WinCC OA config entries -> [ Mod ] -> aliveTimeoutMsg & aliveTimeout

For instance alivecheck with holding register 1001
[mod_3]
aliveTimeoutMsg = 3 1001
#aliveTimeout = 0