Search found 11 matches
- Wed Aug 21, 2019 6:08 pm
- Forum: Bugs / Problems
- Topic: Event-manager memory leak
- Replies: 3
- Views: 4005
Event-manager memory leak
We need to acknowledge alerts from script with additional information in _add_value_7 and _add_value_8. We use function alertSetWait for this (ACK_bug.ctl). It was noticed that in this case there is a memory leak on the event manager. I attached project for demonstration. 1. Run the ACK_bug.ctl scri...
- Tue May 14, 2019 1:18 pm
- Forum: Bugs / Problems
- Topic: OPC HDA server with the "Bounds"option
- Replies: 0
- Views: 7853
OPC HDA server with the "Bounds"option
Good day. We have problems with the request to the OPC HDA server with the "Bounds"option. The HDA server WinCC needs to return the two correct values, but returns null values as "bad." Found problem with clients: WinCC OA OPC HDA Client, Matrikon OPC HDA Explorer. Screenshots of...
- Fri Apr 19, 2019 1:23 pm
- Forum: Bugs / Problems
- Topic: Problem with queries with filters on aliases.
- Replies: 3
- Views: 4162
Re: Problem with queries with filters on aliases.
As I wrote above, just 1 datapoint. And this DP type is not used in other DP types as nested.How many datapoints are defined for the DP type eRemont2?
Yes, we tested this query on different projects, but not with WinCC OA 3.16Can you observe the same behaviour in another system?
- Fri Apr 19, 2019 8:57 am
- Forum: Bugs / Problems
- Topic: Problem with queries with filters on aliases.
- Replies: 3
- Views: 4162
Problem with queries with filters on aliases.
1.png 1.png We have dp type "eRemont2" with only one 1 dp without aliases. "Select alert" from 1 dp takes 1,7 seconds if we use alias filter and don't find alias. SELECT ALERT '_alert_hdl.._ack_state', '_alert_hdl.._ack_time', '_alert_hdl.._add_value_7', '_alert_hdl.._add_value_...
- Wed Mar 06, 2019 3:00 pm
- Forum: Bugs / Problems
- Topic: Retrieving data from the OPC UA server for a time interval in which the connection to the server was lost
- Replies: 4
- Views: 4697
Re: Retrieving data from the OPC UA server for a time interval in which the connection to the server was lost
There is no automatism available which sets the dp element to retrieve historical data. You can implement your own script which performs the following steps -- detect when the connection is lost -- detect when the connection is reestablished -- encode the information and write it to the dp element ...
- Tue Mar 05, 2019 10:34 am
- Forum: Bugs / Problems
- Topic: Retrieving data from the OPC UA server for a time interval in which the connection to the server was lost
- Replies: 4
- Views: 4697
Re: Retrieving data from the OPC UA server for a time interval in which the connection to the server was lost
Historical access is supported by server and I can retrieve data by sending command thru internal datapoint (DPT is _OPCUAServer) For example, Connection to the server was lost between 2019.03.04 19:51:09.000 and 2019.03.04 19:52:10.000. I write command into _OPCUAServerDPname.Command.HistoryRead an...
- Mon Mar 04, 2019 3:04 pm
- Forum: Bugs / Problems
- Topic: Retrieving data from the OPC UA server for a time interval in which the connection to the server was lost
- Replies: 4
- Views: 4697
Retrieving data from the OPC UA server for a time interval in which the connection to the server was lost
Hello, I have problem with automatic retrieving data from the OPC UA server via WinCC OA OPC UA client for a time interval in which the connection to the server was lost. WinCC OA help: "Writing the data to data point element with appropriate peripheral address: This allows to automatically ins...
- Fri Oct 05, 2018 2:10 pm
- Forum: Bugs / Problems
- Topic: Reduce switch time ?f IEC104 driver connections
- Replies: 3
- Views: 4149
Re: Reduce switch time ?f IEC104 driver connections
Thanks for the answer.
We already tried to set different values for connection timeout and use different config entries for the iec section, but did not reach the goal. We managed to make the switching time less than 30 seconds but much longer than necessary (1 second).
We already tried to set different values for connection timeout and use different config entries for the iec section, but did not reach the goal. We managed to make the switching time less than 30 seconds but much longer than necessary (1 second).
- Mon Oct 01, 2018 12:07 pm
- Forum: Bugs / Problems
- Topic: Reduce switch time ?f IEC104 driver connections
- Replies: 3
- Views: 4149
Reduce switch time ?f IEC104 driver connections
<t>Hello.<br/> <br/> Switching to reserve connection of the IEC104 driver takes about 30 seconds. Is it possible to reduce this time to 1 second?<br/> <br/> The configuration of the stand is as follows:<br/> 1. There is an IEC104 connection with two connections.<br/> 2. The connection works in a red...
- Mon Aug 20, 2018 7:11 am
- Forum: Bugs / Problems
- Topic: Problem with setting position for reference panels which were added via addSymbol function
- Replies: 3
- Views: 2510
Re: Problem with setting position for reference panels which were added via addSymbol function
Thanks for reply.
Will it be fixed in 3.15 or I need handle it in code?
Will it be fixed in 3.15 or I need handle it in code?