Hi,
I can able to read and write the digital signals from Modbus RTU. Also in the case of analog signals i can able to read/write the integer values from it, but in float values i cant....i am getting some other values , not the exact one (shows some ranges including negative and positive values), pls give me a solution...is there any coversion is needed?
How to read/write float values in Modbus RTU
- jiji.thankappan
- Posts:44
- Joined: Tue Sep 18, 2018 7:39 am
How to read/write float values in Modbus RTU
- ozangor
- Posts:44
- Joined: Thu Sep 22, 2011 2:57 pm
Re: How to read/write float values in Modbus RTU
Hi there,
It is mostly dependent on the device you are using that serves the information. Try to find configuration in the device of that specific signal, you may find some hint.
In case you require the conversion, you need to add the config "message conversion" to your dp element.
It is mostly dependent on the device you are using that serves the information. Try to find configuration in the device of that specific signal, you may find some hint.
In case you require the conversion, you need to add the config "message conversion" to your dp element.
- Gertjan van Schijndel
- Posts:634
- Joined: Mon Aug 02, 2010 10:37 am
Re: How to read/write float values in Modbus RTU
Has the config entry in my answer from your topic not solved this?
- jiji.thankappan
- Posts:44
- Joined: Tue Sep 18, 2018 7:39 am
Re: How to read/write float values in Modbus RTU
No, i didnt get the exact value...also am trying with byte and word as type of tranformation with msg conversion, again its showing some values ,not the exact one
- marcel@realsolutions.nu
- Posts:12
- Joined: Mon Aug 02, 2010 10:22 am
Re: How to read/write float values in Modbus RTU
Hello,
I'm using modbus driver for float variables, your description seems like an endian mismatch between your device and the WinCC-OA modbus driver
please look into the help, modbus-TCP-driver, config-entries: littleEndianRegister (but I had expected that this byte-swap then also was needed for the integers.... But in modbus devices you can have byte swap in a word/integer, and a word/integer swap in a float....)
Please see attached screenshots for the address-config I've used.... just for your information....
good luck...
I'm using modbus driver for float variables, your description seems like an endian mismatch between your device and the WinCC-OA modbus driver
please look into the help, modbus-TCP-driver, config-entries: littleEndianRegister (but I had expected that this byte-swap then also was needed for the integers.... But in modbus devices you can have byte swap in a word/integer, and a word/integer swap in a float....)
Please see attached screenshots for the address-config I've used.... just for your information....
good luck...