How to get values through Modbus communication

Find and share HowTos to various installations / configurations!
6 posts • Page 1 of 1
jiji.thankappan
Posts:44
Joined: Tue Sep 18, 2018 7:39 am

How to get values through Modbus communication

Post by jiji.thankappan »

Hi all,
am trying to connect my winccoa demo project with an RTU through Modbus driver, its showing some values (not exactly the values stored in RTU) , here am attaching 3 screenshots, pls give me solution for this https://www.winccoa.com/fileadmin/image ... hot_10.png Image Image
Attachments
Screenshot_12.png
Screenshot_11.png
Screenshot_10.png

Gertjan van Schijndel
Posts:634
Joined: Mon Aug 02, 2010 10:37 am

Re: How to get values through Modbus communication

Post by Gertjan van Schijndel »

It looks like you want to read 32bit values from a TBox RTU, which uses big endian. So setting the following config entry should resolve your issue:
[mod]
littleEndianRegister = 0

But to make use of the buffering functionality of the device you could better use the IEC 60870-5-104 or DNP3 protocol.

jiji.thankappan
Posts:44
Joined: Tue Sep 18, 2018 7:39 am

Re: How to get values through Modbus communication

Post by jiji.thankappan »

Thank you.....

jiji.thankappan
Posts:44
Joined: Tue Sep 18, 2018 7:39 am

Re: How to get values through Modbus communication

Post by jiji.thankappan »

Hi Gertjan van Schijndel ,
Thanks for your support.....now i am getting the exact values.... :woohoo:

jiji.thankappan
Posts:44
Joined: Tue Sep 18, 2018 7:39 am

Re: How to get values through Modbus communication

Post by jiji.thankappan »

Hi,
Also in DNP3 I can read and write the analog signal, in the case of digital signal i can read the values from RTU but i can't write ,so can you please give me a solution for how could I write digital output values?

Gertjan van Schijndel
Posts:634
Joined: Mon Aug 02, 2010 10:37 am

Re: How to get values through Modbus communication

Post by Gertjan van Schijndel »

Jiji T S wrote:
Also in DNP3 I can read and write the analog signal, in the case of digital signal i can read the values from RTU but i can't write ,so can you please give me a solution for how could I write digital output values?
You could better open a new topic for this question, since it has nothing to do with Modbus communication. After first looking into the other DNP3 topics.