Cannot manage to transfer configs from a masterdatapoint to its DPEs.

Post by Natty »

Hello,

I developed a WinCC OA (v3.14 - P05) application for the Montparnasse Paris train station. Attached files are the WinCC OA server logs.

I do not manage to transfer configs "_alert_hdl" and "_address" from a masterdatapoint to its DPEs. All the "alert_hdl" configs do appear underneath DPEs. But some DPEs heritate from an activated "alert_hdl" config when other heritate from a deactivated one. "address" configs can't be seen underneath DPE leaf. I have added severeal datapoints last few days and I didn't have this problem.

Log file show :

2018.09.06 09:02:43.143["error==-5 in dpCopy from _mp_HAOT_PT to _mp_Test111.pt"]

WCCOAui (10), 2018.09.06 10:12:19.119, CTRL, SEVERE, 5/ctrl, Location of the following log entry:
Module: Para_61
Panel: C:\\Siemens\\Automation\\WinCC_OA\\3.14\\panels\\para.pnl []
Object: 10 named: "activeX" of type: DP_TREE
Script: OnDpTypeChanged
Library: C:\\Siemens\\Automation\\WinCC_OA\\3.14\\scripts\\libs\\mp.ctl
Line: 1292
WCCOAui (10), 2018.09.06 10:12:19.119, PARAM,SEVERE, 105, Invalid license, DP: System1:_mp_Test111.dsfs.Etat:_address.._type, MAN: (SYS: 1 Event -num 0 CONN: 2)
WCCOAui (10), 2018.09.06 10:12:19.119, CTRL, WARNING, 5/ctrl, Location of the following log entry:
Module: Para_61
Panel: C:\\Siemens\\Automation\\WinCC_OA\\3.14\\panels\\para.pnl []
Object: 10 named: "activeX" of type: DP_TREE
Script: OnDpTypeChanged
Library: C:\\Siemens\\Automation\\WinCC_OA\\3.14\\scripts\\libs\\mp.ctl
Line: 1295
WCCOAui (10), 2018.09.06 10:12:19.119, SYS, WARNING, 0, , Error setting config (1), System1:_mp_Test111.dsfs.Commande:_address.._type, 16
WCCOAui (10), 2018.09.06 10:12:19.119, CTRL, WARNING, 5/ctrl, Location of the following log entry:
Module: Para_61
Panel: C:\\Siemens\\Automation\\WinCC_OA\\3.14\\panels\\para.pnl []
Object: 10 named: "activeX" of type: DP_TREE
Script: OnDpTypeChanged
Library: C:\\Siemens\\Automation\\WinCC_OA\\3.14\\scripts\\libs\\mp.ctl
Line: 1295
WCCOAui (10), 2018.09.06 10:12:19.119, SYS, WARNING, 0, , Error setting config (2), System1:_mp_Test111.dsfs.Commande:_address.._reference, M.1.16.0


Do you know how to solve this problem ? I can send screenshots of the tree if needed.

Thanks in advance.



https://www.winccoa.com/fileadmin/image ... 180906.zip
Attachments
log_20180906.zip
(3.86 MiB) Downloaded 224 times

leoknipp
Posts:2928
Joined: Tue Aug 24, 2010 7:28 pm

Re: Cannot manage to transfer configs from a masterdatapoint to its DPEs.

Post by leoknipp »

You possibly get the log message for the invalid license because you have reached the maximum number of IOs in your project. Activating additional _address configs is not possible in that case.
The limit for the IOs is defined with the license you are using in this project.

Best Regards
Leopold Knipp
Senior Support Specialist

Natty
Posts:34
Joined: Mon May 23, 2016 2:08 pm

Re: Cannot manage to transfer configs from a masterdatapoint to its DPEs.

Post by Natty »

Hello,

Ok. Do you know how I can check the number of IOs used ?

Thank you very much.

Regards

leoknipp
Posts:2928
Joined: Tue Aug 24, 2010 7:28 pm

Re: Cannot manage to transfer configs from a masterdatapoint to its DPEs.

Post by leoknipp »

You can use the I/O counter panel (Lab --> Prototypes) to get the number of active addresses.
https://portal.etm.at/index.php?option= ... &Itemid=79

Best Regards
Leopold Knipp
Senior Support Specialist

Natty
Posts:34
Joined: Mon May 23, 2016 2:08 pm

Re: Cannot manage to transfer configs from a masterdatapoint to its DPEs.

Post by Natty »

Thanks you. One last question, I am using redundant servers and I have a 15 000 IOs license. Does it mean I can only use 7 500 DPE (with an activated address) on each server ?

leoknipp
Posts:2928
Joined: Tue Aug 24, 2010 7:28 pm

Re: Cannot manage to transfer configs from a masterdatapoint to its DPEs.

Post by leoknipp »

No, in a redundant system you can use the number of I/Os defined in the license.
The database is the same on both servers and every server counts therefore the complete number of I/Os.

Best Regards
Leopold Knipp
Senior Support Specialist