Using the S7+ driver . Data points are imported into the project using "TIA importers"
I do get the following messages:
2/s7plus, Requested variable subscriptions count 714 is higher than available limit 400
4/s7plus, Pollgroup _sub_plc1_FB_Inverter failed to establish subscriptions and will use native polling until new reconnect instead
5/s7plus, Ignoring poll request for Pollgroup _sub_plc1_FB_Inverter because last request did not finish yet
Is it possible to increase the limit of variables in subscriptions? Or how best to split the variables into several subscriptions?
S7+ Requested variable subscriptions count is higher than available limit
- o_atlina
- Posts:8
- Joined: Wed Nov 02, 2016 12:18 pm
S7+ Requested variable subscriptions count is higher than available limit
- Gertjan van Schijndel
- Posts:634
- Joined: Mon Aug 02, 2010 10:37 am
Re: S7+ Requested variable subscriptions count is higher than available limit
The only way to increase the subscription limit is to replace the PLC with a faster one/one that can handle more subscriptions.
In the 'Engineering' tab of the PLC configuration panel you can see how many subscriptions the PLC can handle.
To prevent the error messages you could reduce the number of subscriptions. Multiple subscriptions with the same settings can be replaced with a single subscription.
In the 'Engineering' tab of the PLC configuration panel you can see how many subscriptions the PLC can handle.
To prevent the error messages you could reduce the number of subscriptions. Multiple subscriptions with the same settings can be replaced with a single subscription.