We have defined 5 range alarm handling.
How can be changed Alarm limit values and hysteresis values dynamically at runtime by the operator. Is it possible?.
Thank you
Alarm Limit Value Parameter
- leoknipp
- Posts:2928
- Joined: Tue Aug 24, 2010 7:28 pm
Re: Alarm Limit Value Parameter
You can write a script which modifies the values for the attributes by using dpSet()/dpSetWait().
The scripts has to
-- acknowledge all pending alerts for the given dp element
-- deactivate the _alert_hdl config
-- modify the attributes
-- activate the _alert_hdl config
Which attributes need to be modifed depends on the _alert_hdl config which shall be adapted.
Best Regards
Leopold Knipp
Senior Support Specialist
The scripts has to
-- acknowledge all pending alerts for the given dp element
-- deactivate the _alert_hdl config
-- modify the attributes
-- activate the _alert_hdl config
Which attributes need to be modifed depends on the _alert_hdl config which shall be adapted.
Best Regards
Leopold Knipp
Senior Support Specialist
- adaneau
- Posts:310
- Joined: Tue Feb 21, 2012 9:49 am
Re: Alarm Limit Value Parameter
Hi,
I would add a detail about hysteresis: this doesnt exist as attribute, actually this is just a tweak of l_limit and u_limit for each range
BR
Alex
I would add a detail about hysteresis: this doesnt exist as attribute, actually this is just a tweak of l_limit and u_limit for each range
BR
Alex
- hakan
- Posts:28
- Joined: Wed Nov 24, 2010 9:38 am
Re: Alarm Limit Value Parameter
Ok. I developed script. I shared it. Maybe help someone
Code: Select all
main()
{
int rc;
dyn_errClass err;
float hh = 100.0; // from text field
float h = 90.0;// from text field
float l = 30.0;// from text field
float ll = 20.0;// from text field
float hyst = 2.0;// from text field
float a1_u_hyst = ll;
float a2_u_hyst = l;
float a2_l_hyst = ll+hyst;
float a3_u_hyst = h-hyst;
float a3_l_hyst = l+hyst;
float a4_u_hyst = hh-hyst;
float a4_l_hyst = h;
float a5_l_hyst = hh;
dpSetWait(dpPV+":_alert_hdl.._active", FALSE); //alert must be passive
dpSetWait(dpPV+":_alert_hdl.._ack", 1);//alert must be ack
rc = dpSetWait(
dpPV+":_alert_hdl.1._u_limit", ll,
dpPV+":_alert_hdl.2._u_limit", l,
dpPV+":_alert_hdl.2._l_limit", ll,
dpPV+":_alert_hdl.3._u_limit", h,
dpPV+":_alert_hdl.3._l_limit", l,
dpPV+":_alert_hdl.4._u_limit", hh,
dpPV+":_alert_hdl.4._l_limit", h,
dpPV+":_alert_hdl.5._l_limit", hh,
dpPV+":_alert_hdl.1._u_hyst_limit",a1_u_hyst,
dpPV+":_alert_hdl.2._l_hyst_limit",a2_l_hyst,
dpPV+":_alert_hdl.2._u_hyst_limit",a2_u_hyst,
dpPV+":_alert_hdl.3._l_hyst_limit",a3_l_hyst,
dpPV+":_alert_hdl.3._u_hyst_limit",a3_u_hyst,
dpPV+":_alert_hdl.4._l_hyst_limit",a4_l_hyst,
dpPV+":_alert_hdl.4._u_hyst_limit",a4_u_hyst,
dpPV+":_alert_hdl.5._l_hyst_limit",a5_l_hyst,
dpPV+":_alert_hdl.._active", TRUE);
if(rc == 0){
}
else{
ChildPanelOnRelativModal("vision/MessageWarning", "Warning", makeDynString("Wrong Values. Check Parameters"),5,5);
}
err = getLastError();
if(dynlen(err)>0)
{
throwError(err);
}
DebugN("done", rc);
}
- Gertjan van Schijndel
- Posts:634
- Joined: Mon Aug 02, 2010 10:37 am
Re: Alarm Limit Value Parameter
An acknowledge is not always needed. If it is not needed an error message will be written in the log file.
To prevent this you could replace the deactivation and acknowledge 'dpSet' with the function 'dpDeactivateAlert'.
To prevent this you could replace the deactivation and acknowledge 'dpSet' with the function 'dpDeactivateAlert'.