Hi,
Using Wincc OA 3.15 p 010, Windows 10 64 Bit, Tia portal v13, PLC 1500;
We've already imported some tag from a Tia Project, without any problem..
when i need to add another tag, i've to re-import updated Tia project, or i can add it manually on para, writing new symbolic address?
The tag on PLC is added, but i cannot "Resolve symbolic address"
I've already tryed add manually a tag ,but with no luck.
Other options?
Add s7+ symbolic tag without import project again
- andrea.bertorelli
- Posts:33
- Joined: Wed May 31, 2017 3:58 pm
Add s7+ symbolic tag without import project again
- Gertjan van Schijndel
- Posts:634
- Joined: Mon Aug 02, 2010 10:37 am
Re: Add s7+ symbolic tag without import project again
Importing the updated TIA project should solve the error.
It is not possible to manually add a new symbolic address.
With 3.15+P011 (or 3.16) a new symbolic address should be available with online browsing after reconnecting to the PLC.
It is not possible to manually add a new symbolic address.
With 3.15+P011 (or 3.16) a new symbolic address should be available with online browsing after reconnecting to the PLC.