OPC UA Config Import
Postby gozdeunver »
Hello,
We have a problem about OPC UA periphery address config & excel import.
We have inserted periphery address config to masterdatapoint and as item we have entered “ns= ;s=”, then export them to excel.
After configuring addresses in excel for all the datapoints, we import it to the system.
After import part is finished successfully, in the para the power config part of the datapoints seems blank, subscription part is not selected and item part is blank. The panel is attached.
Do you have any opinion with this situation, could you please suggest a way to enter periphery addresses with excel import?
I have tested it using WinCC OA 3.15 + P008 on a Windows 7 machine.
The modified address was imported correctly.
The steps I made are
-- added the master datapoint
-- configure the _address config (OPC UA input simple) for a boolean element
-- right-click at the DP type and choosing the option "Create dplist (1DPE/line)
-- defined a filename
-- started the export
-- start Excel
-- configured the project in the Excel Add-In for the mass configuration
-- loaded the exported ASCII file
-- edited the "Periphery address" for the DP instance (not the master datapoint)
In the first column the information "I" (ignore) switches to "M" (modify)
-- called the function "MaParaSym: Transfer thsi DPList to WinCC OA"
-- confirmed the next dialog with "Yes"
-- waited until the import is finished
-- checked the settings in the Para module
If it does not work please check if there are errors reported during the ASCII import.
Best Regards
Leopold Knipp
Senior Support Specialist