TIA Importer - Problem showing Tags
andrea.bertorelli
Post by andrea.bertorelli »
Wincc OA 3.15 P008 - Windows 10 64bit - Tia portal V14 - Real PLC 1500 - Connected correctly to PLC
I'm trying to import the variables that I've correctly exported from the tia project, with no result.
I can correctly view the project exported from the tia v14 with "SIMATICSCADA_Export_V14" as shown below.
Once the "* .txt" file has been exported to "ProjectName\\data", I do not see any variables.
My TIA project has both data DB and FB with relative DB Instance, and all variables are "visible/writable in HMI"
I followed both the guides inside the "help" and the open questions on the forum, and the following video https://portal.etm.at/movies/WinCC_OA_T ... Import.mp4),
but nothing.
Where am I wrong? https://www.winccoa.com/fileadmin/image ... magine.png
mkerk
Re: TIA Importer - Problem showing Tags
Post by mkerk »
in your screenshot I can´t recognize any structure with the FB data type ! For example in your screenshot the data type (column Data type in the S7+ Symbolic panel) of "BLOCCO_1_DB" is "empty" and NOT an FB. Also all other structures are NOT FBs. This is the reason why the list in the importer Panel is empty. Could you please check the PLC program again.
As written in the WinCC OA documentation: Only FBs and UDTs with one or more instances are displayed by the TIA importer. FBs and UDTs which have no instances are not listed and can therefore not be imported as types only.
BR,
Mousser
andrea.bertorelli
I have imported the tags correctly. The PLC program was correct, but the version was wrong (sw plc v. TIA 14 opened with TIA 14 sp1).
Made with TIA 13 sp1 it worked.
Now we are developing software plc with TIA v15, you know when will be available the software to export the project from the TIA V15?
Andrea