I am having my PLC program in TIA Portal V14 and the SCADA on the Wincc OA.
Is it possible to simulate the Application in Wincc OA from TIA Portal.

I have been developing the application earlier in TIA Portal with Wincc Advance SCADA, and
I use to test both PLC program and SCADA in simulation mode.

Is it same possible in Wincc OA.

Thanks and Regards
Chandan.

Gertjan van Schijndel
Posts:634
Joined: Mon Aug 02, 2010 10:37 am

Re: Simulation in WinCC OA with TIA Portal

Post by Gertjan van Schijndel »

WinCC OA does not have a simulation mode.

For testing how a WinCC OA application responds on values from a PLC it is enough to just write the values on the datapoint elements (which normally gets these values from a PLC).
But also PLCSIM V14 (or newer) could provide the values for the S7+ driver.

Chandan
Posts:12
Joined: Sun Dec 03, 2017 9:58 am

Re: Simulation in Wicc OA with TIA Portal

Post by Chandan »

Hi Expert,
Thanks for the reply below.
I have created the project in the TIA Portal v14.
I want to test this by running the PLC SIM and communicating with WINCC OA.

What are the steps and procedure to do this.
Will be highly obliged if I get some more details on it.


Regards
Chandan.

Gertjan van Schijndel
Posts:634
Joined: Mon Aug 02, 2010 10:37 am

Re: Simulation in Wicc OA with TIA Portal

Post by Gertjan van Schijndel »

It should be straight forward:
1. Set PLC type to 'PLCSim'
2. Set the 'PG/PC Interface' to 'S7ONLINE --> PLCSIM'