OPC UA Datapoint Limitation

Discussions about product bugs & problems!
Note: This is no replacement for the Official ETM Support!
3 posts • Page 1 of 1
paramesh1985
Posts:81
Joined: Thu Sep 25, 2014 6:03 am

OPC UA Datapoint Limitation

Post by paramesh1985 »

Hi ,

Is there any limitation for OPC UA data point read group.

In our project we configured around more than 336666 datapoints are there.

Whenever we are trying to connect via OPC UA browser we are getting memory error.

Its working less than 10K datapoints.

leoknipp
Posts:2928
Joined: Tue Aug 24, 2010 7:28 pm

Re: OPC UA Datapoint Limitation

Post by leoknipp »

Can you please describe the "memory error" in detail.
Which of the processes gets a "memory error"?
Do you get WinCC OA log messages refering to the "memory error"?

Which WinCC OA version and operating system is used?

Best Regards
Leopold Knipp
Senior Support Specialist

RudiKreiner
Posts:198
Joined: Mon May 16, 2011 2:10 pm

Re: OPC UA Datapoint Limitation

Post by RudiKreiner »

This issue appears to be related to this one:
https://portal.etm.at/index.php?option= ... 15&id=6065

Since I was just playing around to see what would happen with very many datapoints, I did not pursue the issue by trying to configure more memory.
Instead I just reduced the number of datapoints in the configuration to the ones that we really needed, which turned out to be less than about 35000.

But maybe the information there can help you too.