Modbus master - slave communication

Find and share HowTos to various installations / configurations!
7 posts • Page 1 of 1
Nikolay
Posts:34
Joined: Tue Aug 21, 2012 7:10 am

Modbus master - slave communication

Post by Nikolay »

Dear colleagues.
I have a problem. I have many controllers (about 100 pieces), these controllers can send telegrams to the system. That is, the Scada System must act as the SLAVE, and the controllers in the role of MASTER. I'm trying to create 1 DPE to listen to all the controllers at the same time, but I can not do it. Help, please, to solve this task.
Thank you in advance.

https://www.winccoa.com/fileadmin/image ... 171211.png
Attachments
3-20171211.png
4.png

Gertjan van Schijndel
Posts:634
Joined: Mon Aug 02, 2010 10:37 am

Re: Modbus master - slave communication

Post by Gertjan van Schijndel »

The Modbus server is better suited for this than the Modbus driver.

Nikolay
Posts:34
Joined: Tue Aug 21, 2012 7:10 am

Re: Modbus master - slave communication

Post by Nikolay »

I'm working in WinCC OA 3.13, and in this version I did not meet the ModBus server. This functionality was added in version 3.15?

leoknipp
Posts:2928
Joined: Tue Aug 24, 2010 7:28 pm

Re: Modbus master - slave communication

Post by leoknipp »

The Modbus server is available since WinCC OA version 3.14.

Best Regards
Leopold Knipp
Senior Support Specialist

Nikolay
Posts:34
Joined: Tue Aug 21, 2012 7:10 am

Re: Modbus master - slave communication

Post by Nikolay »

Installed version 3.14. In the driver settings, a new "Only active driver" menu item has appeared. Is this what I need? In the documentation about this innovation nothing is written. And what should be the Peripheral address configuration for DPE?

leoknipp
Posts:2928
Joined: Tue Aug 24, 2010 7:28 pm

Re: Modbus master - slave communication

Post by leoknipp »

The option "Only active driver" is part of the Modbus TCP client configuration. Also peripheral addresses are only used when configuring a Modbus client.

Data which shall be provided by the WinCC OA Modbus TCP server is defined in a CNS view (Plant Model Editor).

Best Regards
Leopold Knipp
Senior Support Specialist

Nikolay
Posts:34
Joined: Tue Aug 21, 2012 7:10 am

Re: Modbus master - slave communication

Post by Nikolay »

Thank you very much, it's worked! :)