Dear all,
I would like to report an issue that I have recently found during the creation of a Remote UI project with WinCC OA 3.15 Patch 05.
I'm working in VM Ware 12 enviroment, running 2 VMs,:
1. SCADA Server: RHEL 7 with WinCC OA 3.15 P05 installed. Project created is running. Samba is sharing WinCC OA project folder.
2. SCADA Remote UI: Windows 7 Ultimate SP1 with WinCC OA 3.15 P05 installed. Linux share folder is accesible and it is possible to copy&paste the remote project in the same local path that I'm trying to create Remote UI Project with WinCC OA.
The problem is the following:
Everytime I try to create the folder via the wizard, I select the remote path (from SCADA Server), and then create.... it takes a while and then an error comes out: "Error Creating project". You can find the PVSS_II.log in the attachment. It appears to happen only in virtualized enviroment, not in real enviroment. Any ideas would be welcome!
Thank you
WCCOAui (0), 2017.09.28 19:36:43.128, SYS, WARNING, 22/pa, paCreateClientProjExtend, Error when copying the server project '//132.1.1.20/exports/Marmaray_Rev33' to the client project 'C:/WinCC_OA_proj/Marmaray_Rev33'
WCCOAui (0), 2017.09.28 19:38:21.896, CTRL, WARNING, 54, Unexpected state,
Module: WinCC OA ProjectAdministration 3.15
Panel: C:\\Siemens\\Automation\\WinCC_OA\\3.15\\panels\\projAdmin\\project_admin.pnl []
Object: 3 named: "manTable" of type: TABLE
Script: Clicked
Library: C:\\Siemens\\Automation\\WinCC_OA\\3.15\\scripts\\libs\\pmon.ctl
Line: 261, tcpOpen, timeout expired
WCCOAui (0), 2017.09.28 19:38:22.848, CTRL, WARNING, 54, Unexpected state,
Module: WinCC OA ProjectAdministration 3.15
Panel: C:\\Siemens\\Automation\\WinCC_OA\\3.15\\panels\\projAdmin\\project_admin.pnl []
Object: 24 named: "cmdStart" of type: PUSH_BUTTON
Script: Clicked
Library: C:\\Siemens\\Automation\\WinCC_OA\\3.15\\scripts\\libs\\pmon.ctl
Line: 261, tcpOpen, timeout expired
WCCOAui (0), 2017.09.28 19:38:23.184, CTRL, WARNING, 54, Unexpected state,
Module: WinCC OA 3.15
Panel: C:\\Siemens\\Automation\\WinCC_OA\\3.15\\panels\\projAdmin\\console.pnl []
Script: Initialize
Library: C:\\Siemens\\Automation\\WinCC_OA\\3.15\\scripts\\libs\\pmon.ctl
Line: 261, tcpOpen, timeout expired
WinCC OA - Cannot create Remote UI Project
- nmnogueira
- Posts:125
- Joined: Thu May 05, 2011 12:59 pm
Re: WinCC OA - Cannot create Remote UI Project
Try to start the WinCC OA Project Administration by choosing "Run as Administrator"
- KimiK
- Posts:4
- Joined: Thu Oct 06, 2016 7:32 pm
Re: WinCC OA - Cannot create Remote UI Project
As simple as that 
Thanks Nuno!
Thanks Nuno!
- agruber
- Posts:147
- Joined: Tue Sep 07, 2010 2:52 pm
Re: WinCC OA - Cannot create Remote UI Project
Depending on what you want to achieve with the Remote UI you could also use the Desktop UI instead, which should be much easier to setup.
BR, Andreas
Customer Care
BR, Andreas