Ascii Manager Errors
Postby ewoenne »
Hi, I'm having issues with the Ascii Manager on v3.15 Patch 3.
Creating and trying to save a new configuration with multiple filters set produces the error below. It seems to work with just Datapoints selected and then once a configuration has saved I can add extra filters and DPs to it successfully.
Can you please give us the information which options you have selected and which steps are necessary to get this error.
At my tests I did not get the log message.
Best Regards
Leopold Knipp
Senior Support Specialist
I selected 2 DP types, chose Set/clear all filters and entered in the new ascii file and configuration name. Pressing the save button produces the error.
Testing it again now, I found that selecting all the filters individually (instead of choosing the Set/clear all button) does not produce the error!
Thanks for the information, now I could reproduce the error. The problem is that the entries in the dp list are not correct when activating/deactivating the option to set all filters.
I've fixed the problem. The bugfix will be part of the next patch for WinCC OA 3.15.
Best Regards
Leopold Knipp
Senior Support Specialist