Want to implement Oracle (RDB) query with live alarms
fmulder
Post by fmulder »
We want to develop a ‘Dashboard’ that takes data from Oracle to show the amount of live alarms per station. Can anyone tell me : when is an alarm actually being stored in Oracle. Right away or when the alarm is closed ?
Could you explain : how many records are being stored for an alarm. We believe that it is : CAME, WENT and ACK. Is this correct ? are there 3 records per alarm or more
Does anyone have a query that gives us a list with live alarms ( all CAME’s and the unack’s )
Frenk Mulder
Share the fun
Re: Want to implement Oracle (RDB) query with live alarms
I got the following answers from the developer:
The alarms are stored at least every 3 three seconds (per default, or setting the flushInterval in the RDBParameterization panel) the records are stored to Oracle.
There are records stored per alarm (1 CAME, 1 WENT, the acknowledge updates the existing record).
If you do a dpQuery-Call in a Ctrl-Script (RDB-Project) and enable -dbg 2 for the UI you will find the correct SQL-Stmt for Oracle.
To be honest I do not exactly know which alarms are shown in the Alert-Screen.
agruber
Post by agruber »
Maybe there is a good reason for you to go with a direct Oracle connection, but why don't you go directly to WinCC OA. I can imagine, you run such a dashboard in a Web environment (a browser), in that case, you could use our webserver. You can even use spontaneous data with websockets if your client supports that (current browsers do), example here:
Integrate values from WinCC OA to any w ... Websockets
BR,