[Bug Report] GEDI not updating #uses
7 posts • Page 1 of 1
elvir.brkic@bstelecom.ba
Post by elvir.brkic@bstelecom.ba »
There is a bug in version 3.14 (P004) with following symptoms.
Prerequisites:
We need two libraries that contain function with same name, and another script that is calling that function. In included example there is lib_a.ctl, lib_b.ctl and test panel that is calling function on click. https://www.winccoa.com/fileadmin/image ... es_bug.zip
Symptoms:
1. First issue is that panel will not call function from library selected with #uses, but will use wrong library.
Steps to reproduce:
a. Edit panel script to use lib_a.ctl
b. Restart GEDI
c. Run panel in QuickTest and panel will call function from lib_a.ctl which is OK.
d. Now edit panel to use lib_b.ctl instead, and run in QuickTest. Panel will call function from lib_b.ctl which is also OK.
e. Edit panel again to use lib_a.ctl and run QuickTest. Panel will call function from lib_b.ctl, which is NOT OK.
It is necessary to restart GEDI again i order for it to work properly. This is not specific only to GEDI, we can use any other panel as parent that would open test panel as a child.
So basically, we can only change library once, and than we are stuck until parent panel is restarted.
2. Second issue is cosmetic but is causing confusion, because tool-tip for function will remember only one library as location of function (where "Jump to function" points to), and will not update if we use #uses to switch to different library even after GEDI restart.
uses_bug.zip
(850 Bytes) Downloaded 132 times
Re: [Bug Report] GEDI not updating #uses
I do not see this as a bug.
Once a library is loaded in a manager it remains loaded until the manager is stopped. Only closing a panel where #uses was used does not unload the libraries.
Using the same function names in different libraries might not only be a problem during runtime if a manager loads both libraries. Also debugging the code or trying to find an error will be more difficult if you do not know exactly which libraries have been loaded at the time when the error occured.
Please use unique function names to avoid these problems.
What I see as a "bug" is inconsistent behavior between 1.d. and 1.e.
If we load libA during startup, why would it allow us to switch to libB during runtime, and not allow us to switch back to libA?
Also, there is still issue 2. which can not be resolved with GEDI restart.
In the end we started using unique names, but it feels more like workaround because it defeats purpose of #uses.
if a library is already loaded it is not loaded again. Therefore the functions are not replaced in your example by those defined in iibA when using #uses again.
If several libraries contain functions with same names those are used which have been loaded last.
The GEDI is searching in all libraries for matching functions, independent of the fact if the library is loaded (during startup or with the #uses keyword) or not.
"The GEDI is searching in all libraries for matching functions, independent of the fact if the library is loaded (during startup or with the #uses keyword) or not."
To be exact, the script editor loads all libraries to know which functions are existing in which libs.
However, the script editor does currently not deal with duplicate function names. It stores all names in a hash and only the last one inserted is known.
Call it limitation or bug ...
However, note that the UI and CTRL manager CAN NOT USE duplicate functions in different libraries loaded at the same time.
Just the last one will be found.
That's neither a bug nor a limitation.
By defintion, all functions in all loaded libraries MUST BE UNIQUE.
#uses just tells the CTRL interpreter core which lib to load. It never unloads libs during runtime.
We can call it "undocumented feature" for now :)
I must say I was not aware of this "By definition, all functions in all loaded libraries MUST BE UNIQUE" and I couldn't find it in help.
IMHO, it should be better documented, but it would be nice if script editor could perform some validity check (hash is already there :)).
I think that for me all of confusion was caused because keyword #uses is somewhat misleading. It just loads a library and has no effect on which library will be actually used by script.
Not that this will matter with unique names anyway.
Anyway, thank you Leopold and Martin for detailed explanation.
For the first issue (execution) you could try to use 'execScript' or 'evalScript' and include the '#uses' in the passed script.