I have the facing the following problems with DNP3 configuration and will appreciate support from the forum experts:
1 - In PVSS, where is the DNP3 Master address defined? This is the address to which the RTU should send its unsolicited responses.
2 - How is the configuration of Binary Command done in PVSS to latch/unlatch an internal RTU point? I have created a complex datapoint with the elements as described in PVSS Help, and I have assigned the Subindex to each element. But PVSS is generating following errror when I change the "original" value:
"PVSS00dnp3 (1), 2011.05.03 10:00:28.000, PARAM,SEVERE, 54, Unexpected state, Dnp3IDPOutstation, brmCallbackFcn, Outstation DNP3Ethernet: Request timeout"
Attached is screenshot of CROB complex Datatype parameterization
Thanks and Regards
DNP3 configuration
Re: DNP3 configuration
a detailled description for the configuration of the DNP3-driver can be found at the PVSS/WinCC OA online help (installed with the product on your computer) at the chapter Drivers --> DNP3.
Can you please have a look at this description.
If you need further assistance please refer to the common support to get an answer to your questions.
If you have a valid support contract with us, please contact us at: support_pvss@etm.at.
When sending the support request please write in the topic of the mail that the question is related to WinCC OA or PVSS.
- GPSAUTO
Hi
You need to add the following to the config file, Master address (My address was 1)
[dnp3]
LinkAddress = 1;
Also see bitmap for DNP3 parameterization info
The error you are getting indicates that the master is not communicating with the RTU
The State should indicate connected
Regards
Bill
[dnp3]
LinkAddress = 1;
Regards
Bill