Hi there!
I have a project where I need to integrate a Siemens LOGO! (PLC slave) with WinCC OA as the SCADA system.
The SCADA server will be running on RHEL 6.5 or later.
The following is the specifications of the PLC:
CPU: 230RC AC/DC 115~240, digital input 8 (AC/DC), digital output 4 (Relay 5A)
Expansion: DM8 230R digital input 4 (AC/DC), digital output 4 (Relay 5A)
Can I know what is the most efficient and cost effective way to integrate this PLC to WinCC OA?
What are drivers I would need to purchase?
Thank you.
Garry
Integration between Siemens LOGO! and WinCC OA
- shotdunyun
- Posts:10
- Joined: Mon Nov 03, 2014 3:30 am
Integration between Siemens LOGO! and WinCC OA
- Gertjan van Schijndel
- Posts:634
- Joined: Mon Aug 02, 2010 10:37 am
Re: Integration between Siemens LOGO! and WinCC OA
I think the only way is to use the S7 driver, but you will need to do some work in the logo it get it working.
As an alternative you could also use a S7-1200, then you do not need any work for the communication in the plc (only a minor configuration change).
As an alternative you could also use a S7-1200, then you do not need any work for the communication in the plc (only a minor configuration change).
- leoknipp
- Posts:2928
- Joined: Tue Aug 24, 2010 7:28 pm
Re: Integration between Siemens LOGO! and WinCC OA
Hello,
this posting was moved to the "Features / Solutions"-section.
Please note that the "Questions / Answers"-section is only related to the WinCC OA user days.
Best Regards
Leopold Knipp
Senior Support Specialist
this posting was moved to the "Features / Solutions"-section.
Please note that the "Questions / Answers"-section is only related to the WinCC OA user days.
Best Regards
Leopold Knipp
Senior Support Specialist
- shotdunyun
- Posts:10
- Joined: Mon Nov 03, 2014 3:30 am
Re: Integration between Siemens LOGO! and WinCC OA
Thanks for the tip Gertjan.
Garry
Garry
- Vanagonjon
- Posts:4
- Joined: Thu Jan 22, 2015 2:46 pm
Re: Integration between Siemens LOGO! and WinCC OA
I am interested in connecting a logo to the S7 driver. Has anyone successfully done this?
- alug
- Posts:42
- Joined: Mon Oct 18, 2010 11:00 am
Re: Integration between Siemens LOGO! and WinCC OA
Hi,
LOGO PLCs will be supported in the upcoming WinCC OA 3.15 version
best regards
Andreas
LOGO PLCs will be supported in the upcoming WinCC OA 3.15 version
best regards
Andreas
- Vanagonjon
- Posts:4
- Joined: Thu Jan 22, 2015 2:46 pm
Re: Integration between Siemens LOGO! and WinCC OA
Hi Andreas,
Thanks for the quick response. Why are the features I want always a cycle away = )
Will integration be through the same S7 driver, or will there be a new driver specifically for the LOGO? Which memory areas will we be able to access?
Jon
Thanks for the quick response. Why are the features I want always a cycle away = )
Will integration be through the same S7 driver, or will there be a new driver specifically for the LOGO? Which memory areas will we be able to access?
Jon
- Gertjan van Schijndel
- Posts:634
- Joined: Mon Aug 02, 2010 10:37 am
Re: Integration between Siemens LOGO! and WinCC OA
If you cannot wait until 3.15 is released you can also use 3.12 with at least patch 26.
It is integrated in the S7 driver. You will need to configure the LOGO! for S7 communication, it includes also the addresses which can be read/written.
It is integrated in the S7 driver. You will need to configure the LOGO! for S7 communication, it includes also the addresses which can be read/written.