Hello.
Is it possible to connect a S7-1500 to WINCC OA 3.11.1? And how to do it? I switched the DBs to non optimized DBs but I even cannot connect to the CPU. Is there any way to do this?
Thanks.
WINCC OA and S7-1500
- Gertjan van Schijndel
- Posts:634
- Joined: Mon Aug 02, 2010 10:37 am
Re: WINCC OA and S7-1500
You need to enable "Allow PUT/GET Communication" (under the CPU Protection properties in V12/V13) and the driver connects faster when you use the s7 config entry 'UseConnections = 1'.
- funkey
- Posts:85
- Joined: Mon Dec 27, 2010 1:11 pm
Re: WINCC OA and S7-1500
Thanks for your answer. I found out how it works already yesterday. I cannot swith to 'UseConnections = 1' because of 22 other PLCs and huge amounts of data that I could not receive with one connection every two seconds. I don't think this setting can be set for every PLC!?
- Gertjan van Schijndel
- Posts:634
- Joined: Mon Aug 02, 2010 10:37 am
Re: WINCC OA and S7-1500
The 'useConnections = 1' cannot be set for a single PLC. What you can do is to add a s7 driver with this setting for the S7-1500.