DPE'S comming of PLC to configure alerts

Discussion about recent product features & solutions!
3 posts • Page 1 of 1
ccmelo
Posts:4
Joined: Mon Oct 13, 2025 4:00 pm

DPE'S comming of PLC to configure alerts

Post by ccmelo »

Its possible to defined a DPE for the limiting values on the alert handling?

In my case, I have the limiting values coming from PLC and I need to configure the alert in WinCC OA using the parameters from PLC.
Attachments
imagem (1).png
imagem (1).png (10.97 KiB) Viewed 591 times

leoknipp
Posts:2928
Joined: Tue Aug 24, 2010 7:28 pm

Re: DPE'S comming of PLC to configure alerts

Post by leoknipp »

There is no standard solution to assign thresholds defined in the PLC to the _alert_hdl config.
If you want to apply the configuration from the PLC you have to implement a function on your own which maps the values from the PLC to the _alert_hdl configuration.

Best Regards
Leopold Knipp
Senior Support Specialist

gschijndel
Posts:376
Joined: Tue Jan 15, 2019 3:12 pm

Re: DPEs coming of PLC to configure alerts

Post by gschijndel »

As a workaround you could generate the alerts in the PLC (a boolean for each alert range) or use a multi-instance alert and raise/lower the alerts with scripting.