Redundant Modbus Driver Status

Post by n_lev »

Hi!


I am setting up a system where the server has two ethernet cards and a PLC it is talking to is a redundant pair and each PLC has two ethernet cards as well.
I've configured the Modbus driver as per image attached
Image

Question 1:
For this I have disabled the redundant PLC in the Modbus driver configuration (it's currently not available to me). This seem to work. For example If I pull the cable out of PLC1 Ethernet1 card, I can see pmon messages that the system lost connection to 163.189.12.56 and established connection to 163.189.13.56. Graphics continue to work.
What I need to do now is to be able to report on the status of all these network connections. I looked in the internal datapoint "_Mod_Plc_1", there is ConnStatus and Error tags (see attached image)
Image
but they seem pretty general and I really want to know the status of all 4 connections (active, standby, broken). Is there a way do achieve this?

Question 2:
If I re-enable the redundant PLC in the Modbus driver configuration I get the following bevaviour:
1. Pmon keeps messaging that both connections to the redundant PLC failed (that part is probably OK)
2. If I look at the DP in the PARA I can see that the invalid bits of the DP come on and off all the time (which incidentally makes all my graphic objects flash invalid all the time). This is actually not good, the whole idea is that the system should operate even if one of the redundant PLC is dead. Am I doing something wrong? Image

Gertjan van Schijndel
Posts:634
Joined: Mon Aug 02, 2010 10:37 am

Re: Redundant Modbus Driver Status

Post by Gertjan van Schijndel »

1. Looks to be a limitation of the driver.
2. Seems to be a bug.
For both you should contact ETM to confirm this and get a fix.

leoknipp
Posts:2928
Joined: Tue Aug 24, 2010 7:28 pm

Re: Redundant Modbus Driver Status

Post by leoknipp »

Hello,

the image with your configuration was not attached to your posting, therefore I couldn't have a look at it.
At the internal datapoint only the connection status to the PLC is written to.

If you need further assistance please send an official support request to the e-mail address support.automation@siemens.com. At the topic please include the information about the product WinCC OA including the version information. Also please attach the shield file you are using.

Best Regards
Leopold Knipp
Senior Support Specialist