Configure Modbus Redundancy Alerts

Find and share HowTos to various installations / configurations!
2 posts • Page 1 of 1
emaddocks
Posts:83
Joined: Tue Sep 04, 2018 12:50 am

Configure Modbus Redundancy Alerts

Post by emaddocks »

Hi,

Does anyone know how to configure alerts for when one of the redundant hosts configured in the Modbus PLC configuration loses connection?

Does the Modbus driver provide this functionality? I haven't been able to find anything that looks like it would in the internal _Mod_Plc DPT.

Cheers
Eric

leoknipp
Posts:2928
Joined: Tue Aug 24, 2010 7:28 pm

Re: Configure Modbus Redundancy Alerts

Post by leoknipp »

The connection state for a PLC connection is written to the "ConnState" element for the _Mod_Plc datapoint.
Detailed information can be found in the WinCC OA Documentation:
https://www.winccoa.com/documentation/W ... naldp.html

Best Regards
Leopold Knipp
Senior Support Specialist