OPC UA SERVER PROBLEMS

Discussions about product bugs & problems!
Note: This is no replacement for the Official ETM Support!
2 posts • Page 1 of 1
orla090978
Posts:55
Joined: Thu Jan 03, 2019 2:05 pm

OPC UA SERVER PROBLEMS

Post by orla090978 »

Good afternoon,

in WinCC OA project 3.16 P015 we added OPC UA server driver for unsafe connection.
When we connect our OPC UA server with client we found these issues:

SEVERE, 15/opcuasrv, OpcUaSManager in Funktion transformO2P, 0 kann nicht von OpcUa zu PVSS transformiert werden

Are there some parameters useful to permit the correct transformation of data from Client to server inside WINCC OA?

Thanks a lot.
Best regards

leoknipp
Posts:2928
Joined: Tue Aug 24, 2010 7:28 pm

Re: OPC UA SERVER PROBLEMS

Post by leoknipp »

According to the source code this log message is written if the datatype of the OPC item cannot be mapped to a WinCC OA datatype.
The information "0" seems to be the datatype.

If you want to have information for a log message please always copy the full content of the log message.

Best Regards
Leopold Knipp
Senior Support Specialist