in WinCC OA project 3.16 P015 we added OPC UA server driver for unsafe connection.
When we connect our OPC UA server with client we found these issues:
SEVERE, 15/opcuasrv, OpcUaSManager in Funktion transformO2P, 0 kann nicht von OpcUa zu PVSS transformiert werden
Are there some parameters useful to permit the correct transformation of data from Client to server inside WINCC OA?
Thanks a lot.
Best regards
OPC UA SERVER PROBLEMS
- leoknipp
- Posts:2928
- Joined: Tue Aug 24, 2010 7:28 pm
Re: OPC UA SERVER PROBLEMS
According to the source code this log message is written if the datatype of the OPC item cannot be mapped to a WinCC OA datatype.
The information "0" seems to be the datatype.
If you want to have information for a log message please always copy the full content of the log message.
Best Regards
Leopold Knipp
Senior Support Specialist
The information "0" seems to be the datatype.
If you want to have information for a log message please always copy the full content of the log message.