Duplicate a large number of DPE

Find and share HowTos to various installations / configurations!
11 posts • Page 1 of 2
andrea.bertorelli
Posts:33
Joined: Wed May 31, 2017 3:58 pm

Duplicate a large number of DPE

Post by andrea.bertorelli »

Hi,
i am trying to replicate my DP structures (now created for plc1 only) for more plc. I exported the configuration of all DPEs starting with "plc1*" from ASCII and replaced it with "plc2". Imported the variables log show me a lot of errors that repeats itself indefinitely for almost all the DPEs.

I use the 3.17 patch 05, the DPEs I export are about 32.000 of which about 1000 are connected with s7plus, the others are "internal". Almost all of them have the _general property active which I use to store descriptions in the dyn_langString.

Also I noticed that in PROJ_PATH/db/ winccoa/ Ive very big databases, could it be a storage limit of these databases?
"textvar.db" 699.052KB
"dynvar.db" 299.595KB
"objNameTxt.db" 147.839KB

Code: Select all

WCCILdata    (0), 2021.01.23 12:24:41.933, SYS,  SEVERE,     69, Database error, PersGeneralConfig, storeConfig ,Speicherfehler Config
WCCILdata    (0), 2021.01.23 12:24:41.933, PARAM,WARNING,    22, Internal consistency check for config failed, DataManager, handleValueChangeMsg, Config was not stored correctly (code 4): 
System1:plc2_IST_MULTIMETRO.DATI.Tensione_L2L3:_general.._type (Type: 311 Sys: 1 Dp: 20847 El: 14 : _general.._type)
WCCILdata    (0), 2021.01.23 12:24:41.933, SYS,  SEVERE,     69, Database error, DataManTask, dbError, RAIMA Database Error *** Code:-901 (INTERNAL error: -901
bad dchain
C errno = 0: No error
FILE: ..\..\..\ExternLibs\rdm45\runtime\Dio.c(2270))
WCCILdata    (0), 2021.01.23 12:24:41.933, SYS,  SEVERE,     69, Database error, PersGeneralConfig, storeConfig ,Speicherfehler Config
WCCILdata    (0), 2021.01.23 12:24:41.934, PARAM,WARNING,    22, Internal consistency check for config failed, DataManager, handleValueChangeMsg, Config was not stored correctly (code 4): 
System1:plc2_IST_MULTIMETRO.DATI.Tensione_L3L1:_general.._type (Type: 311 Sys: 1 Dp: 20847 El: 15 : _general.._type)
WCCILdata    (0), 2021.01.23 12:24:41.934, SYS,  SEVERE,     69, Database error, DataManTask, dbError, RAIMA Database Error *** Code:-901 (INTERNAL error: -901
bad dchain
C errno = 0: No error
FILE: ..\..\..\ExternLibs\rdm45\runtime\Dio.c(2270))
WCCILdata    (0), 2021.01.23 12:24:41.934, SYS,  SEVERE,     69, Database error, PersGeneralConfig, storeConfig ,Speicherfehler Config
WCCILdata    (0), 2021.01.23 12:24:41.934, PARAM,WARNING,    22, Internal consistency check for config failed, DataManager, handleValueChangeMsg, Config was not stored correctly (code 4): 
System1:plc2_IST_MULTIMETRO.DATI.Corrente_N:_general.._type (Type: 311 Sys: 1 Dp: 20847 El: 12 : _general.._type)
WCCILdata    (0), 2021.01.23 12:24:41.934, SYS,  SEVERE,     69, Database error, DataManTask, dbError, RAIMA Database Error *** Code:-901 (INTERNAL error: -901
bad dchain
C errno = 0: No error
FILE: ..\..\..\ExternLibs\rdm45\runtime\Dio.c(2270))

CCILdata    (0), 2021.01.23 12:24:41.935, SYS,  SEVERE,     69, Database error, PersGeneralConfig, storeConfig ,Speicherfehler Config
WCCILdata    (0), 2021.01.23 12:24:41.935, PARAM,WARNING,    22, Internal consistency check for config failed, DataManager, handleValueChangeMsg, Config was not stored correctly (code 4): 
System1:plc2_IST_MULTIMETRO.DATI.Tensione_L3N:_general.._type (Type: 311 Sys: 1 Dp: 20847 El: 18 : _general.._type)
WCCILdata    (0), 2021.01.23 12:24:42.194, IMPL, SEVERE,     54, Unexpected state, PersDpConfig, setAttribute, TYPE_ATTR erwartet: 
System1:plc2_IST_MULTIMETRO.DATI.PotenzaReattiva:_general.._bool_01 (Type: 311 Sys: 1 Dp: 20847 El: 21 : _general.._bool_01)
BIT_VAR 262144 0
WCCILdata    (0), 2021.01.23 12:24:42.194, PARAM,WARNING,    22, Internal consistency check for config failed, DataManager, handleValueChangeMsg, Config was not stored correctly (code 4): 
System1:plc2_IST_MULTIMETRO.DATI.PotenzaReattiva:_general.._bool_01 (Type: 311 Sys: 1 Dp: 20847 El: 21 : _general.._bool_01)
WCCILdata    (0), 2021.01.23 12:24:42.195, IMPL, SEVERE,     54, Unexpected state, PersDpConfig, setAttribute, TYPE_ATTR erwartet: 
System1:plc2_IST_MULTIMETRO.DATI.PotenzaApparente:_general.._bool_01 (Type: 311 Sys: 1 Dp: 20847 El: 22 : _general.._bool_01)
BIT_VAR 262144 0
WCCILdata    (0), 2021.01.23 12:24:42.195, PARAM,WARNING,    22, Internal consistency check for config failed, DataManager, handleValueChangeMsg, Config was not stored correctly (code 4): 
System1:plc2_IST_MULTIMETRO.DATI.PotenzaApparente:_general.._bool_01 (Type: 311 Sys: 1 Dp: 20847 El: 22 : _general.._bool_01)
WCCILdata    (0), 2021.01.23 12:24:42.195, IMPL, SEVERE,     54, Unexpected state, PersDpConfig, setAttribute, TYPE_ATTR erwartet: 
System1:plc2_IST_MULTIMETRO.DATI.EnergiaAttiva_M:_general.._bool_01 (Type: 311 Sys: 1 Dp: 20847 El: 25 : _general.._bool_01)
BIT_VAR 262144 0

andrea.bertorelli
Posts:33
Joined: Wed May 31, 2017 3:58 pm

Re: Duplicate a large number of DPE

Post by andrea.bertorelli »

EDIT:

Hi,
I noticed that going to modify the _general of the old DPEs, Ive errors that make me think that there is some corrupted database, below the log trying to modify the _general of a DPE from PARA.

Code: Select all

WCCILevent   (0), 2021.01.24 12:08:10.929, SYS,  WARNING,    65, Wrong destination address, (SYS: 1 Driver -num 1 CONN: 1), DP_MSG_SIMPLE_REQUEST
WCCILevent   (0), 2021.01.24 12:08:10.929, SYS,  WARNING,    65, Wrong destination address, (SYS: 1 Driver -num 1 CONN: 1), DP_MSG_SIMPLE_REQUEST
WCCOAui      (2), 2021.01.24 12:08:10.930, SYS,  SEVERE,     38, Message could not be sent, DP: System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_address.._type, MAN: (SYS: 1 Driver -num 1 CONN: 1), Could not send message DP_MSG_SIMPLE_REQUEST #58923
WCCOAui      (2), 2021.01.24 12:08:10.930, SYS,  SEVERE,     38, Message could not be sent, DP: System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_cmd_conv.._type, MAN: (SYS: 1 Driver -num 1 CONN: 1), Could not send message DP_MSG_SIMPLE_REQUEST #58923
WCCOAui      (2), 2021.01.24 12:08:10.930, SYS,  SEVERE,     38, Message could not be sent, DP: System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_msg_conv.._type, MAN: (SYS: 1 Driver -num 1 CONN: 1), Could not send message DP_MSG_SIMPLE_REQUEST #58923
WCCOAui      (2), 2021.01.24 12:08:10.930, SYS,  SEVERE,     38, Message could not be sent, DP: System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_smooth.._type, MAN: (SYS: 1 Driver -num 1 CONN: 1), Could not send message DP_MSG_SIMPLE_REQUEST #58923
WCCILdata    (0), 2021.01.24 12:08:15.572, SYS,  SEVERE,     69, Database error, DataManTask, dbError, RAIMA Database Error *** Code:-901 (INTERNAL error: -901
bad dchain
C errno = 0: No error
FILE: ..\..\..\ExternLibs\rdm45\runtime\Dio.c(2270))
WCCILdata    (0), 2021.01.24 12:08:15.573, SYS,  SEVERE,     69, Database error, PersGeneralConfig, storeConfig, Speicherfehler Variable
WCCILdata    (0), 2021.01.24 12:08:15.573, PARAM,WARNING,    22, Internal consistency check for config failed, DataManager, handleValueChangeMsg, Config was not stored correctly (code 4): 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._langString_03 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._langString_03)
WCCILdata    (0), 2021.01.24 12:08:15.573, IMPL, SEVERE,     54, Unexpected state, PersDpConfig, setAttribute, TYPE_ATTR erwartet: 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._langString_04 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._langString_04)
LANGTEXT_VAR 2621440 42
LANG:10029 ""
LANG:10028 ""
LANG:10021 ""
LANG:10015 ""
LANG:10000 ""
...
WCCILdata    (0), 2021.01.24 12:08:15.573, PARAM,WARNING,    22, Internal consistency check for config failed, DataManager, handleValueChangeMsg, Config was not stored correctly (code 4): 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._langString_04 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._langString_04)
WCCILdata    (0), 2021.01.24 12:08:15.574, IMPL, SEVERE,     54, Unexpected state, PersDpConfig, setAttribute, TYPE_ATTR erwartet: 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._langString_05 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._langString_05)
LANGTEXT_VAR 2621440 42
...

WCCILdata    (0), 2021.01.24 12:08:15.574, PARAM,WARNING,    22, Internal consistency check for config failed, DataManager, handleValueChangeMsg, Config was not stored correctly (code 4): 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._langString_05 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._langString_05)
WCCILdata    (0), 2021.01.24 12:08:15.574, IMPL, SEVERE,     54, Unexpected state, PersDpConfig, setAttribute, TYPE_ATTR erwartet: 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._blob_01 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._blob_01)
BLOB_VAR 3014656 Blob encountered with 0 items, dump follows
WCCILdata    (0), 2021.01.24 12:08:15.574, PARAM,WARNING,    22, Internal consistency check for config failed, DataManager, handleValueChangeMsg, Config was not stored correctly (code 4): 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._blob_01 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._blob_01)
WCCILdata    (0), 2021.01.24 12:08:15.574, IMPL, SEVERE,     54, Unexpected state, PersDpConfig, setAttribute, TYPE_ATTR erwartet: 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._blob_02 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._blob_02)
BLOB_VAR 3014656 Blob encountered with 0 items, dump follows
WCCILdata    (0), 2021.01.24 12:08:15.574, PARAM,WARNING,    22, Internal consistency check for config failed, DataManager, handleValueChangeMsg, Config was not stored correctly (code 4): 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._blob_02 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._blob_02)
WCCILdata    (0), 2021.01.24 12:08:15.575, IMPL, SEVERE,     54, Unexpected state, PersDpConfig, setAttribute, TYPE_ATTR erwartet: 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._blob_03 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._blob_03)
BLOB_VAR 3014656 Blob encountered with 0 items, dump follows
WCCILdata    (0), 2021.01.24 12:08:15.575, PARAM,WARNING,    22, Internal consistency check for config failed, DataManager, handleValueChangeMsg, Config was not stored correctly (code 4): 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._blob_03 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._blob_03)
WCCILdata    (0), 2021.01.24 12:08:15.575, IMPL, SEVERE,     54, Unexpected state, PersDpConfig, setAttribute, TYPE_ATTR erwartet: 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._blob_04 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._blob_04)
BLOB_VAR 3014656 Blob encountered with 0 items, dump follows
WCCILdata    (0), 2021.01.24 12:08:15.575, PARAM,WARNING,    22, Internal consistency check for config failed, DataManager, handleValueChangeMsg, Config was not stored correctly (code 4): 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._blob_04 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._blob_04)
WCCILdata    (0), 2021.01.24 12:08:15.575, IMPL, SEVERE,     54, Unexpected state, PersDpConfig, setAttribute, TYPE_ATTR erwartet: 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._blob_05 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._blob_05)
BLOB_VAR 3014656 Blob encountered with 0 items, dump follows
WCCILdata    (0), 2021.01.24 12:08:15.576, PARAM,WARNING,    22, Internal consistency check for config failed, DataManager, handleValueChangeMsg, Config was not stored correctly (code 4): 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._blob_05 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._blob_05)
WCCILdata    (0), 2021.01.24 12:08:15.576, IMPL, SEVERE,     54, Unexpected state, PersDpConfig, setAttribute, TYPE_ATTR erwartet: 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._long_01 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._long_01)
LONG_VAR 4587520 0
WCCILdata    (0), 2021.01.24 12:08:15.576, PARAM,WARNING,    22, Internal consistency check for config failed, DataManager, handleValueChangeMsg, Config was not stored correctly (code 4): 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._long_01 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._long_01)
WCCILdata    (0), 2021.01.24 12:08:15.576, IMPL, SEVERE,     54, Unexpected state, PersDpConfig, setAttribute, TYPE_ATTR erwartet: 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._long_02 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._long_02)
LONG_VAR 4587520 0
WCCILdata    (0), 2021.01.24 12:08:15.576, PARAM,WARNING,    22, Internal consistency check for config failed, DataManager, handleValueChangeMsg, Config was not stored correctly (code 4): 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._long_02 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._long_02)
WCCILdata    (0), 2021.01.24 12:08:15.576, IMPL, SEVERE,     54, Unexpected state, PersDpConfig, setAttribute, TYPE_ATTR erwartet: 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._long_03 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._long_03)
LONG_VAR 4587520 0
WCCILdata    (0), 2021.01.24 12:08:15.577, PARAM,WARNING,    22, Internal consistency check for config failed, DataManager, handleValueChangeMsg, Config was not stored correctly (code 4): 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._long_03 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._long_03)
WCCILdata    (0), 2021.01.24 12:08:15.577, IMPL, SEVERE,     54, Unexpected state, PersDpConfig, setAttribute, TYPE_ATTR erwartet: 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._long_04 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._long_04)
LONG_VAR 4587520 0
WCCILdata    (0), 2021.01.24 12:08:15.577, PARAM,WARNING,    22, Internal consistency check for config failed, DataManager, handleValueChangeMsg, Config was not stored correctly (code 4): 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._long_04 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._long_04)
WCCILdata    (0), 2021.01.24 12:08:15.577, IMPL, SEVERE,     54, Unexpected state, PersDpConfig, setAttribute, TYPE_ATTR erwartet: 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._long_05 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._long_05)
LONG_VAR 4587520 0
WCCILdata    (0), 2021.01.24 12:08:15.577, PARAM,WARNING,    22, Internal consistency check for config failed, DataManager, handleValueChangeMsg, Config was not stored correctly (code 4): 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._long_05 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._long_05)
WCCILdata    (0), 2021.01.24 12:08:15.578, IMPL, SEVERE,     54, Unexpected state, PersDpConfig, setAttribute, TYPE_ATTR erwartet: 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._ulong_01 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._ulong_01)
ULONG_VAR 4784128 0
WCCILdata    (0), 2021.01.24 12:08:15.578, PARAM,WARNING,    22, Internal consistency check for config failed, DataManager, handleValueChangeMsg, Config was not stored correctly (code 4): 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._ulong_01 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._ulong_01)
WCCILdata    (0), 2021.01.24 12:08:15.578, IMPL, SEVERE,     54, Unexpected state, PersDpConfig, setAttribute, TYPE_ATTR erwartet: 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._ulong_02 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._ulong_02)
ULONG_VAR 4784128 0
WCCILdata    (0), 2021.01.24 12:08:15.578, PARAM,WARNING,    22, Internal consistency check for config failed, DataManager, handleValueChangeMsg, Config was not stored correctly (code 4): 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._ulong_02 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._ulong_02)
WCCILdata    (0), 2021.01.24 12:08:15.578, IMPL, SEVERE,     54, Unexpected state, PersDpConfig, setAttribute, TYPE_ATTR erwartet: 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._ulong_03 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._ulong_03)
ULONG_VAR 4784128 0
WCCILdata    (0), 2021.01.24 12:08:15.578, PARAM,WARNING,    22, Internal consistency check for config failed, DataManager, handleValueChangeMsg, Config was not stored correctly (code 4): 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._ulong_03 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._ulong_03)
WCCILdata    (0), 2021.01.24 12:08:15.579, IMPL, SEVERE,     54, Unexpected state, PersDpConfig, setAttribute, TYPE_ATTR erwartet: 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._ulong_04 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._ulong_04)
ULONG_VAR 4784128 0
WCCILdata    (0), 2021.01.24 12:08:15.579, PARAM,WARNING,    22, Internal consistency check for config failed, DataManager, handleValueChangeMsg, Config was not stored correctly (code 4): 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._ulong_04 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._ulong_04)
WCCILdata    (0), 2021.01.24 12:08:15.579, IMPL, SEVERE,     54, Unexpected state, PersDpConfig, setAttribute, TYPE_ATTR erwartet: 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._ulong_05 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._ulong_05)
ULONG_VAR 4784128 0
WCCILdata    (0), 2021.01.24 12:08:15.579, PARAM,WARNING,    22, Internal consistency check for config failed, DataManager, handleValueChangeMsg, Config was not stored correctly (code 4): 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._ulong_05 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._ulong_05)
WCCILdata    (0), 2021.01.24 12:08:15.579, IMPL, SEVERE,     54, Unexpected state, PersDpConfig, setAttribute, TYPE_ATTR erwartet: 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._bit64_01 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._bit64_01)
ULONG_VAR 4784128 0
WCCILdata    (0), 2021.01.24 12:08:15.579, PARAM,WARNING,    22, Internal consistency check for config failed, DataManager, handleValueChangeMsg, Config was not stored correctly (code 4): 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._bit64_01 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._bit64_01)
WCCILdata    (0), 2021.01.24 12:08:15.580, IMPL, SEVERE,     54, Unexpected state, PersDpConfig, setAttribute, TYPE_ATTR erwartet: 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._bit64_02 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._bit64_02)
ULONG_VAR 4784128 0
WCCILdata    (0), 2021.01.24 12:08:15.580, PARAM,WARNING,    22, Internal consistency check for config failed, DataManager, handleValueChangeMsg, Config was not stored correctly (code 4): 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._bit64_02 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._bit64_02)
WCCILdata    (0), 2021.01.24 12:08:15.580, IMPL, SEVERE,     54, Unexpected state, PersDpConfig, setAttribute, TYPE_ATTR erwartet: 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._bit64_03 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._bit64_03)
ULONG_VAR 4784128 0
WCCILdata    (0), 2021.01.24 12:08:15.580, PARAM,WARNING,    22, Internal consistency check for config failed, DataManager, handleValueChangeMsg, Config was not stored correctly (code 4): 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._bit64_03 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._bit64_03)
WCCILdata    (0), 2021.01.24 12:08:15.580, IMPL, SEVERE,     54, Unexpected state, PersDpConfig, setAttribute, TYPE_ATTR erwartet: 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._bit64_04 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._bit64_04)
ULONG_VAR 4784128 0
WCCILdata    (0), 2021.01.24 12:08:15.581, PARAM,WARNING,    22, Internal consistency check for config failed, DataManager, handleValueChangeMsg, Config was not stored correctly (code 4): 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._bit64_04 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._bit64_04)
WCCILdata    (0), 2021.01.24 12:08:15.581, IMPL, SEVERE,     54, Unexpected state, PersDpConfig, setAttribute, TYPE_ATTR erwartet: 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._bit64_05 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._bit64_05)
ULONG_VAR 4784128 0
WCCILdata    (0), 2021.01.24 12:08:15.581, PARAM,WARNING,    22, Internal consistency check for config failed, DataManager, handleValueChangeMsg, Config was not stored correctly (code 4): 
System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_general.._bit64_05 (Type: 428 Sys: 1 Dp: 15467 El: 2453 : _general.._bit64_05)


andrea.bertorelli
Posts:33
Joined: Wed May 31, 2017 3:58 pm

Re: Duplicate a large number of DPE

Post by andrea.bertorelli »

EDIT 2:

I tried using the guide "How to initialize the configuration history?" , which seems to "shift" the problem, if before the errors came out in the middle of duplication now they come out towards the end of the duplication.
It seems strange to me that I exceeded 16,000,000 ID, during import (-in export_configs.asc -inactivateAlert) in the logviewer the list of variables had reached an ID of 309,000, far from the maximum limit

After RAIMA initialization, and the duplication attempt, the largest database file is objNameTxt.db with 147.839KB, and the others are 20mb or less

leoknipp
Posts:2928
Joined: Tue Aug 24, 2010 7:28 pm

Re: Duplicate a large number of DPE

Post by leoknipp »

The log message
WCCILdata (0), 2021.01.23 12:24:41.933, SYS, SEVERE, 69, Database error, DataManTask, dbError, RAIMA Database Error *** Code:-901 (INTERNAL error: -901
bad dchain
C errno = 0: No error
FILE: ..\..\..\ExternLibs\rdm45\runtime\Dio.c(2270))

refers to some problem in the database.
Some information in the database is corrupted and therefore you get this error.

If you want to get detailed information please get in contact with your common WinCC OA support as there need be done detailed analysis to get information for the cause of the problem.

The log messages
WCCILevent (0), 2021.01.24 12:08:10.929, SYS, WARNING, 65, Wrong destination address, (SYS: 1 Driver -num 1 CONN: 1), DP_MSG_SIMPLE_REQUEST
..
WCCOAui (2), 2021.01.24 12:08:10.930, SYS, SEVERE, 38, Message could not be sent, DP: System1:plc1_IST_DATI_JES.DATI.GenVolt_L3_N:_address.._type, MAN: (SYS: 1 Driver -num 1 CONN: 1), Could not send message DP_MSG_SIMPLE_REQUEST #58923


describe that information cannot be read because there is no driver with number 1 running in your system.
If you start the required the drivers in your project these log message will not occur anymore.

Best Regards
Leopold Knipp
Senior Support Specialist

andrea.bertorelli
Posts:33
Joined: Wed May 31, 2017 3:58 pm

Re: Duplicate a large number of DPE

Post by andrea.bertorelli »

Thanks for the reply!

I was able to solve most of the errors by reloading a very old backup, but I still have problems that Im convinced are related to the general dyn_langString.

Starting from a working project, after initializing the database with the guide, Ive create a simple code that instantiates a list of about 10-15 elements in Italian lang in about 20-25.000 dpes.
And at the end of this process all these errors pop up.

The alarms described below are also "alarm" type, but I assure you that the problem arises only when I do the dpSet of the:

DPE +":_ general.._ dyn_langString"

Code: Select all

WCCILdata    (0), 2021.01.26 10:38:33.659, PARAM,WARNING,    22, Internal consistency check for config failed, DataManager, handleValueChangeMsg, Config was not stored correctly (code 4): 
System1:plc1_VALVE_TCVx56_Vapore.SGN.ALL_ZT:_general.._langString_04 (Type: 292 Sys: 1 Dp: 21303 El: 50 : _general.._langString_04)
WCCILdata    (0), 2021.01.26 10:38:33.659, IMPL, SEVERE,     54, Unexpected state, PersDpConfig, setAttribute, TYPE_ATTR erwartet: 
System1:plc1_VALVE_TCVx56_Vapore.SGN.ALL_ZT:_general.._langString_05 (Type: 292 Sys: 1 Dp: 21303 El: 50 : _general.._langString_05)
LANGTEXT_VAR 2621440 42

Code: Select all

System1:plc1_ALL_CONTATORI.WRN_FTx78:_alert_hdl.._active (Type: 429 Sys: 1 Dp: 19856 El: 16 : _alert_hdl.._active)
WCCILdata    (0), 2021.01.26 10:25:15.238, SYS,  SEVERE,     69, Database error, DataManTask, dbError, RAIMA Database Error *** Code:-909 (SYSTEM/OS error: -909
file record limit exceeded
C errno = 0: No error
FILE: ..\..\..\ExternLibs\rdm45\runtime\Dio.c(2096))
WCCILdata    (0), 2021.01.26 10:25:15.239, SYS,  SEVERE,     69, Database error, DataManTask, dbError, RAIMA Database Error *** Code:-909 (SYSTEM/OS error: -909
file record limit exceeded
C errno = 0: No error
FILE: ..\..\..\ExternLibs\rdm45\runtime\Dio.c(2096))
WCCILdata    (0), 2021.01.26 10:25:15.239, SYS,  SEVERE,     69, Database error, DataManTask, dbError, RAIMA Database Error *** Code:-909 (SYSTEM/OS error: -909
file record limit exceeded
C errno = 0: No error
FILE: ..\..\..\ExternLibs\rdm45\runtime\Dio.c(2096))
WCCILdata    (0), 2021.01.26 10:25:15.239, SYS,  SEVERE,     69, Database error, DataManTask, dbError, RAIMA Database Error *** Code:-909 (SYSTEM/OS error: -909
file record limit exceeded
C errno = 0: No error
FILE: ..\..\..\ExternLibs\rdm45\runtime\Dio.c(2096))
WCCILdata    (0), 2021.01.26 10:25:15.239, IMPL, SEVERE,     54, Unexpected state, PersAlertValue, storeBinaryConfig, getTextAttribut oder storeTextAttribut failed

Code: Select all

plc1_MERKER.WRN_LSHx61:_alert_hdl (Type: 0 Sys: 0 Dp: 1062 El: 32 : _alert_hdl..0)
WCCILdata    (0), 2021.01.26 10:23:07.350, IMPL, WARNING,   187, DP: plc1_MERKER.WRN_LSHx61:_alert_hdl: No gone alert between two came ones at 2020.12.30 11:49:20.165 and 2021.01.26 09:33:02.427, AlertAdministration, insertAlert
WCCILdata    (0), 2021.01.26 10:23:07.354, PARAM,WARNING,    46, Attribute was not archived, ManagerInitialiserfillAckAH, Notification class not found - Standard class is being used
plc1_MERKER.ALL_DispG:_alert_hdl (Type: 0 Sys: 0 Dp: 1062 El: 38 : _alert_hdl..0)
WCCILdata    (0), 2021.01.26 10:23:07.354, IMPL, WARNING,   187, DP: plc1_MERKER.ALL_DispG:_alert_hdl: No gone alert between two came ones at 2021.01.11 12:22:32.638 and 2021.01.26 09:33:02.443, AlertAdministration, insertAlert
WCCILdata    (0), 2021.01.26 10:23:07.355, PARAM,WARNING,    46, Attribute was not archived, ManagerInitialiserfillAckAH, Notification class not found - Standard class is being used

kilianvp
Posts:443
Joined: Fri Jan 16, 2015 10:29 am

Re: Duplicate a large number of DPE

Post by kilianvp »

It looks like you have that Problem:
https://www.winccoa.com/knowledge-base/ ... e-909.html

As soon as you have more than 16777216 entries, this error message appears.

andrea.bertorelli
Posts:33
Joined: Wed May 31, 2017 3:58 pm

Re: Duplicate a large number of DPE

Post by andrea.bertorelli »

Hi!
Thanks for the reply, I had found this thread too, but it didn't provide any tips on how to fix the problem. I was hoping to find some more help here on the forum.

I'll try to contact support!

leoknipp
Posts:2928
Joined: Tue Aug 24, 2010 7:28 pm

Re: Duplicate a large number of DPE

Post by leoknipp »

The log messages you have posted refer to different problems, therefore you will need several solutions to fix all the problems which appeared.

The cause for one problem (file record limit exceeded) is described in the Knowledge Base article. As it can have different reasons (different database parts can be affected) for the log message there is no solution provided in the Knowledge Base article.

Best Regards
Leopold Knipp
Senior Support Specialist

andrea.bertorelli
Posts:33
Joined: Wed May 31, 2017 3:58 pm

Re: Duplicate a large number of DPE

Post by andrea.bertorelli »

I will shortly send a small report of our problem to the support.

I just wanted to clarify that in reality the problems described above only appear when (in order) we reach the limit of the file. As if properties such as address, alert, pv_range etc ... are also corrupted.

In fact, for these tests we used a program that has been installed for several months and works correctly in all its functions, but if we simply go to massively duplicate the DPEs, properties that previously worked correctly are corrupted. (look for address and alert errors).

It will be interesting to understand what happens!!

Thank you all :geek:

adaneau
Posts:310
Joined: Tue Feb 21, 2012 9:49 am

Re: Duplicate a large number of DPE

Post by adaneau »

Hi,

This sounds a lot like you are filling up the configuration history there.

Did you try to import your tags with -noAlertConfigHist ?

11 posts • Page 1 of 2