Hi,
we communicate with PLC CPU 1517 with two through CPs S7 plus driver (WinCC OA 3.16 P15 through subscrition). All is fine untill yesterday when PLC guys had downloaded HW configuration in PLC (without any changing about our IP address).
After this operation our SCADA seems OK (in S7 + configuration driver, CPU and Cp are all OK) but WDOG value from PLC was freezed (we had solved with S7 plus driver restarting; unfortunately we didn't look a WinCC OA log).
How is possible that HW configuration downloading causes this S7 plus driver malfunction?
Thanks in advance.
Regards.
S7 plus driver weirh behaviour after HW download
- orla090978
- Posts:55
- Joined: Thu Jan 03, 2019 2:05 pm
S7 plus driver weirh behaviour after HW download
- leoknipp
- Posts:2928
- Joined: Tue Aug 24, 2010 7:28 pm
Re: S7 plus driver weirh behaviour after HW download
You can have a look at the PVSS_II.log file to see if a log message for the S7+ driver was reported before you have restarted the driver.
Normally it should be necessary to restart the driver when the configuration was downloaded to the PLC.
Best Regards
Leopold Knipp
Senior Support Specialist
Normally it should be necessary to restart the driver when the configuration was downloaded to the PLC.
Best Regards
Leopold Knipp
Senior Support Specialist
- orla090978
- Posts:55
- Joined: Thu Jan 03, 2019 2:05 pm
Re: S7 plus driver weirh behaviour after HW download
Ok thanks Leopold.
Best regards.
Best regards.