is there a way to speed up the fail over from the main to there secondary server ? I have a redundant system running with 3.16 on Linux servers, currently the time to failover to the second server is approx 8-9 seconds. Is that possible to have a faster failover ? I was looking to config options such as aliveTimeout or similar. Our specs calls for 5 sec or less failover time.
Thank You,
Speed up redundant failover
Re: Speed up redundant failover
The time for the redundancy switch needs to take into account 2 parts:
-- Time to detect that the redundant server was lost
-- Time to execute the redundancy switch
Before we can tell you how to speed up the redundancy switch in your case we need to have more detailed information.
Possibly in that special case it is easier if you get in contact with your common WinCC OA support.
- walterd
The failover is quite fast is the first part, the detection that is causing problems. The moment the network is lost I takes 8 sec approx to start the failover, during this time the system is irresponsive.
The aliveTimeout is one of the parameter I was looking into, I have attached my config for reference
- Attachments
- config.zip
- (943 Bytes) Downloaded 401 times
- walterd
Re: Speed up redundant failover - SOLVED
FYI,
Problem solved changing in the config file , aliveTimeout = -3 (or 3 ,see the help for the difference) in [data] and [event]
For a detection of a lost connection between redundant servers you have to set the aliveTimeout for the [event] and [redu] section.
An entry in the [redu] section is necessary as the Redu Manager is also sending alive message to the redundant partner.
Please take into account that you must not use a timeout shorter than 3 seconds.
Before decreasing the timeouts you have to ensure that have a reliable and fast network with low latency times. If the network quality is not good, e.g. delayed transmission of packages, the system will possibly detect a loss of connection even if the network connection was not broken.
For the Data Manager [data] you must not use such a short timeout. Possibly during the recovery (when huge file information is transmitted via WinCC OA messages) the system will detect a timeout.