Double lines with redundancy network connections aren't showed properly in the System Overview
- maherhodali
- Posts:27
- Joined: Tue Aug 07, 2018 10:21 am
Double lines with redundancy network connections aren't showed properly in the System Overview
We are testing redundancy network connections using IPs address in the same network segment, when we use Windows 10 only one line is showed but the redundancy works fine. If the IPs are in different segments both lines are showed correctly. In other environment with Windows Server 2016 this problem does not occur.
- leoknipp
- Posts:2928
- Joined: Tue Aug 24, 2010 7:28 pm
Re: Double lines with redundancy network connections aren't showed properly in the System Overview
When using redundant network connections in WinCC OA you have to define the entries in the config file for the project and the hosts file of the operating system.
Have you done the configuration like it is described in the WinCC OA Documentation for "Redundant network connections"?
Did you check with a ping and disconnecting the networks that they work correctly on operating system level?
Best Regards
Leopold Knipp
Senior Support Specialist
Have you done the configuration like it is described in the WinCC OA Documentation for "Redundant network connections"?
Did you check with a ping and disconnecting the networks that they work correctly on operating system level?
Best Regards
Leopold Knipp
Senior Support Specialist
- maherhodali
- Posts:27
- Joined: Tue Aug 07, 2018 10:21 am
Re: Double lines with redundancy network connections aren't showed properly in the System Overview
yes, those tests were done, with the OS Server 2016 the information (System Overview) is showed correctly, the problem is with OS Windows 10
- leoknipp
- Posts:2928
- Joined: Tue Aug 24, 2010 7:28 pm
Re: Double lines with redundancy network connections aren't showed properly in the System Overview
In the PVSS_II.log file you will see when the network connections are established.
When looking at the file you should see the log entries for the connection between the redundant systems. Maybe you can find in the log files information why the connection was not established.
If you want to have more detailed information for the connections which are established you can use the report flag "-report dispatch" for the Event- and Redu-Manager.
When using the Proxy-Manager you can also get information for the connections in the Proxy Manager using the report flag "-report dispatch".
To get information when connections are established you can use the debug flag "-dbg dispatch".
Best Regards
Leopold Knipp
Senior Support Specialist
When looking at the file you should see the log entries for the connection between the redundant systems. Maybe you can find in the log files information why the connection was not established.
If you want to have more detailed information for the connections which are established you can use the report flag "-report dispatch" for the Event- and Redu-Manager.
When using the Proxy-Manager you can also get information for the connections in the Proxy Manager using the report flag "-report dispatch".
To get information when connections are established you can use the debug flag "-dbg dispatch".
Best Regards
Leopold Knipp
Senior Support Specialist
- gschijndel
- Posts:376
- Joined: Tue Jan 15, 2019 3:12 pm
Re: Double lines with redundancy network connections aren't showed properly in the System Overview
If the network connections are in the same network segment you cannot be sure that both network connections are used, because the OS decides over which connection it sends the data and the WinCC OA will close the second connection from the same source IP address.
Check your logs to see if this is the case.
To see a redundant network use an actual redundant network.
Check your logs to see if this is the case.
To see a redundant network use an actual redundant network.
- Akram
- Posts:8
- Joined: Mon Aug 06, 2018 1:41 pm
Re: Double lines with redundancy network connections aren't showed properly in the System Overview
The problem is not from the configuration , since as shown it is working fine with OS Server 2016 , the problem is when using OS Windows 10 .
Any advice ?
Any advice ?
- leoknipp
- Posts:2928
- Joined: Tue Aug 24, 2010 7:28 pm
Re: Double lines with redundancy network connections aren't showed properly in the System Overview
Did you check the log entries in the PVSS_II.log file when the system is started and tries to establish the connections to the redundant server?
Have you been using the debug flag "-dbg dispatch" to get detailed information for the connections?
Possibly you get in contact with your common WinCC OA support to get assistance.
Best Regards
Leopold Knipp
Senior Support Specialist
Have you been using the debug flag "-dbg dispatch" to get detailed information for the connections?
Possibly you get in contact with your common WinCC OA support to get assistance.
Best Regards
Leopold Knipp
Senior Support Specialist