IEC 61850 originCategory

Discussions about product bugs & problems!
Note: This is no replacement for the Official ETM Support!
2 posts • Page 1 of 1
adam.kapala@croonwolterendros.nl
Posts:1
Joined: Thu Jun 06, 2019 8:33 am

IEC 61850 originCategory

Post by adam.kapala@croonwolterendros.nl »

I want to change the originCategory of the IEC 61850 messages to automatic-remote (number 6). I guess I need to change config of the driver and the user bit 6 as per help file.

I have IEC 61850 drivers 2 and 3. How can I insert the config entry and where to insert it? I tried inserting it into config file of the project with [iec61850] but it is not recognized. Is there a special place for driver config or how should I do it?

Adam

rglock
Posts:19
Joined: Wed Sep 08, 2010 9:54 am

Re: IEC 61850 originCategory

Post by rglock »

Hello,

here's an example:

[iec61850]
originatorCategory = 3

Wenn executing a command (=dpSet on the datapoint-element, containing the output address), you'll have to set the Userbit6 in addition.

You can check the command output, by setting -dbg DEBUG_DRV_COMMAND at the driver.

If you have any further problems with the iec61850-configuration (or in case of possible product/driver problems), please submit an official servicerequest.

best regards
Rainer Glocknitzer