Can't ack alarm

Discussions about product bugs & problems!
Note: This is no replacement for the Official ETM Support!
3 posts • Page 1 of 1
jonred
Posts:36
Joined: Mon Mar 06, 2017 10:24 am

Can't ack alarm

Post by jonred »

Hi,

there are several alarms in a project than can't be acknowledged. When triying to ack, via aescreen or para, we get a "this is not the oldest alert - is not possible to acknowledge" (the message is in spanish, perhaps the message is not exact).
i've tried to deactivate and activate the alarm, change the alarm good range and type. i've also used the setAlert function as showed in help, with no effect.

¿How can i solve this problem?

Thanks

leoknipp
Posts:2928
Joined: Tue Aug 24, 2010 7:28 pm

Re: Can't ack alarm

Post by leoknipp »

When starting the project you will probably see a log message written by the Data Manager with the log text "no gone alert between two came ones".
The problem can be solved with the option -repair alerts for the Data Manager.

https://www.winccoa.com/knowledge-base/ ... e478fd6c34

Best Regards
Leopold Knipp
Senior Support Specialist

jonred
Posts:36
Joined: Mon Mar 06, 2017 10:24 am

Re: Can't ack alarm

Post by jonred »

Hi,

Sorry i didn't mention it, but that was my first step. We had "sttuborn" alarms before and we fix them with this option, but now is not working.

Thnak you