In my project we have configured more than 10 archive manager, while starting the project few managers does not start its throwing the warning message in the log viewer. Please check .
Log files attached.
regards,
r.paramesh
Archive Manager Starting problem
- paramesh1985
- Attachments
- ArchiveLog.txt
- (3.33 KiB) Downloaded 249 times
Re: Archive Manager Starting problem
The log messages describe that some information is missing.
To check if the archives can start with the current configuration you can
-- Stop the project
-- Delete or rename the db/wincc_oa/VA_<num> folder for those archives which do not start
-- Start the project
Then check again if the archives start correctly.
The log file shows archive numbers up to 34.
Are you starting 34 archive managers?
-- Stop the project
- paramesh1985
Thanks. I will check.
yes we are starting 34 archive manager.
regards,
r.paramesh
regards,
r.paramesh
Starting 34 archive managers is not the normal use case.
Please check the configuration of the project and the size of every archive. Probably the configuration can be changed and the number of archive managers can be reduced.
If you need further assistance please get in contact with your common WinCC OA support.