I am using WiccOA 3.11 with Sitras RSC, I am not able to do time synchronization of RTU over IEC 104.
Please suggest the steps for time synchronization over IEC 104.
Time Syschoronization OF IEC 104 slaves
- shashi.kant@siemens.com
- Posts:1
- Joined: Fri Mar 15, 2019 12:47 pm
Time Syschoronization OF IEC 104 slaves
- leoknipp
- Posts:2928
- Joined: Tue Aug 24, 2010 7:28 pm
Re: Time Syschoronization OF IEC 104 slaves
If you want to synchronize the PLC you have to ensure that the config entry timeSync = "Y" is set for the IEC driver.
To do the time synchronization you have to send a message of type 103,C_CS_NA_1.
For details please have a look at the WinCC OA Documentation.
Best Regards
Leopold Knipp
Senior Support Specialist
To do the time synchronization you have to send a message of type 103,C_CS_NA_1.
For details please have a look at the WinCC OA Documentation.