Database has not been repaired - shutdown initiated

Discussions about product bugs & problems!
Note: This is no replacement for the Official ETM Support!
Search

Post Reply
2 posts • Page 1 of 1
EER
Posts: 13
Joined: Fri Jun 12, 2015 1:31 pm

Database has not been repaired - shutdown initiated

Post by EER »

Hi,

I encouter some problems with the database after the database manager is killed (forced reboot or powerloss).
The project is created using PVSS 3.6-SP2 and has been upgraded to WinCCOA 3.18.

When the data manager is killed and restarted with the

Code: Select all

-repair on
argument it fails as shown in the logs:

Code: Select all

....
....
dbRepair:Copyright (C) 1984-1997, Raima Corporation, All Rights Reserved
WCCILdata    (0), 2021.09.21 10:40:49.884, SYS,  SEVERE,     54, Unexpected state, DataManager, systemCall, C:\Siemens\Automation\WinCC_OA\3.18\bin\dbcheck -a -k -t C:\PVSS_projects\my-example\db\wincc_oa\TypeAndId returned exit code 1
WCCILdata    (0), 2021.09.21 10:40:49.889, SYS,  SEVERE,    106, Database repair, DataManager, repairDBase (on), Database could not be repaired
dbRepair:----------------------------------------------------------------------
dbRepair:Processing key file: sysId.key(12), total of 1 node
dbRepair:------------------------------------------------------------------------
dbRepair:Processing key file: dpId.key(13), total of 64 nodes
dbRepair:------------------------------------------------------------------------
dbRepair:Processing key file: confId.key(14), total of 1 node
dbRepair:------------------------------------------------------------------------
dbRepair:Processing key file: fixId.key(15), total of 1 node
dbRepair:------------------------------------------------------------------------
dbRepair:Processing key file: aliasId.key(16), total of 51 nodes
dbRepair:------------------------------------------------------------------------
dbRepair:Processing key file: viewId.key(19), total of 1 node
dbRepair:------------------------------------------------------------------------
dbRepair:Processing data file: pvssGlobal.db(0), total of 1 record
dbRepair:------------------------------------------------------------------------
dbRepair:Processing data file: objName.db(1), total of 10698 records
dbRepair:------------------------------------------------------------------------
dbRepair:Processing data file: objNameTxt.db(2), total of 11984 records
dbRepair:------------------------------------------------------------------------
dbRepair:Processing data file: typeId.db(3), total of 357 records
dbRepair:------------------------------------------------------------------------
dbRepair:Processing data file: elId.db(4), total of 5707 records
dbRepair:------------------------------------------------------------------------
dbRepair:Processing data file: sysId.db(5), total of 2 records
dbRepair:------------------------------------------------------------------------
dbRepair:Processing data file: dpId.db(6), total of 1936 records
dbRepair:------------------------------------------------------------------------
dbRepair:Processing data file: confId.db(7), total of 24 records
dbRepair:------------------------------------------------------------------------
dbRepair:Processing data file: attrId.db(8), total of 519 records
dbRepair:Problems at record 1:
dbRepair:  * set DPATTRIBUTESET(4) error:
dbRepair:    member has null previous-pointer but is not first member
dbRepair:Problems at record 15:
dbRepair:  * set DPATTRIBUTESET(4) error:
dbRepair:    member has null next-pointer but is not last member
...
...
And eventualy:

Code: Select all

dbRepair:46 errors were encountered in 46 records/nodes
WCCILdata0:"C:\\PVSS_projects\\TRVL36\\db\\wincc_oa\\TypeAndId"...FAILED (check)
WCCILdata    (0), 2021.09.21 10:40:51.075, SYS,  FATAL,     106, Database repair, DataManager, repairDBase, Database has not been repaired - shutdown initiated
Does anyone have an idea how to fix this. I wanted to try

Code: Select all

PVSStoolRepairDb 
but this tool seems to be removed from the new WinCCOA release.

User avatar
leoknipp
Posts: 2645
Joined: Tue Aug 24, 2010 7:28 pm

Re: Database has not been repaired - shutdown initiated

Post by leoknipp »

Please take into account that WinCC OA needs to be stopped properly before shutting down the computer. This needs to be done to ensure that the WinCC OA database and also other parts of the system do not get damaged.
In a plant environment it is recommend to use a UPS.

There is no guarantee that the WinCC OA project can be started if a loss of power occured. Sometimes it can happen that the database is damaged and cannot be repaired anymore.
In such a case you have to install a backup of the database.

Information for the Operating Conditions for WinCC OA you can find in the WinCC OA Documentation:
https://www.winccoa.com/documentation/W ... tions.html

During the renaming of PVSS to WinCC OA all executables have been renamed. Therefore, you cannot find the tool PVSStoolRepairDb anymore. The new name is WCCOAtoolRepairDb.

Best Regards
Leopold Knipp
Senior Support Specialist